1 - 16 of 16 Posts
Hi All,
First, thanks to everyone as this is the first time posting and this site has provided quite a bit of valuable information for me in the past. Now it's almost 90 degrees out and I cannot get my A/C to properly function and it's pretty hot in here to say the least.
This past Winter I replaced a White Rogers 1F78 (5/2) thermostat with a Honeywell Prestige thermostat. Heating works perfectly and the new thermostat (with remote) allows me to properly heat my newborn's room. When installing I noticed that there was a separate set of wires (white and red) that I'm assuming are routed up to the A/C unit on the roof -- note that I'm in a large condo building. When installing the thermostat for heating, these were not used and I'm sure this is the reason for my A/C not properly functioning.
When I select "Cool" on the new thermostat the fan comes on, but does not blow cold air. I ran up the roof confirming that the A/C unit was not powered on.
The original thermostat was wired with the following:
Grey cable:
Brown -- Not used
Yellow -- Not used
Green -- Green terminal
Red -- Red terminal (w/ jumper to RC)
White -- White terminal
White cable (one not currently used):
Red -- Yellow terminal
White -- Twisted with blue wire from grey cable
The furnace was wired with the following:
Grey cable:
Yellow -- Yellow terminal
Red -- Red terminal
Blue -- Common terminal
The current thermostat was wired with the following:
Grey cable:
Brown -- Common terminal
White cable -- not used
The current furnace has the following:
Grey cable:
Red -- Red terminal
Below are some pics for reference.
Old thermostat terminals:
New thermostat terminals:
Current furnace terminals:
Any suggestions?
Thank you!
Hvac Pro
I would be VERY VERY careful with what you do in a condo. You need to know for SURE those are the wires etc. If you hookup something wrong and things get damaged the property manager will be all over you for liability reasons. I would talk to them and see if they have a maintenance dept or guy or company they use and go thru the proper channels.
You can take a close up picture of wires in the board?
Look at this thermostat is set to heart (O/B) no colling
Discussion Starter · #8 ·
Close-up on the new thermostat? If so, see
According to the Honeywell install directions, it should be the following for a 1H/1C system (two transformers):
C -- 24VAC common
R -- Power (heating)
Rc -- Power (cooling)
W -- Heat Relay
Y -- Compressor Contacts
G -- Fan Relay
Discussion Starter · #9 ·
Yuri,
When the new tstat was installed, there was no terminal for those A/C wires and they were left not connected to anything. I can't recall why it was left this way.
The original config had the red wire from the A/C going to the yellow terminal on the tstat and had the white wire from the A/C twisted with the blue wire connecting to the common terminal on the furnace. Scratching my head of why this worked with the old tstat. Note that I haven't tried this on the new worried that it might cause more harm than good.
Just an FYI, after we moved into our unit we noticed that there were some oddities on how things were installed. We later learned that not the best contractors were used. Maybe the original setup was an easier way of doing things to make their lives easier...
Thx
Did you test all wires for continuity? It Seems that Yellow was replaced in the old configuration for some reason.
Hvac Pro
You can hook it up the way it was B4. It is a bush league hacker way but they saved wire by not having to run it the extra distance to the furnace.:wink:
Discussion Starter · #12 ·
yuri,
Bush league -- sounds about right for my building :)
JJBoy, yes all wires were tested.
What are your thoughts on just running the red wire (from the A/C) directly to the yellow terminal on the tstat without the twisting the white wire (from the A/C) to the blue wire to be run back to the common terminal on the furnace?
Thx
Hvac Pro
AC needs to be connected to Y and C at the tstat or furnace. Won't run w/o a C connection. Don't twist it. Poor connection will overload the transformer. Need to use a #29 or 31 marette or solder and tape the connection. Y and C need to go to the furnace also. Y starts the furnace fan on newer units G does it on very old ones and C is the return/neutral line.
Discussion Starter · #14 ·
Thanks.
Sorry for the amateur questions, but what if I left my current common wire setup the way it is and soldered the A/C white to the blue wire and connected the blue wire along with the current common wire (brown) to the common terminal on the furnace?
Thx again!
Hvac Pro
All I can do is go with the pic of the tstat subbase which is wired correctly. I cannot see the rest of the wires from here or the control board clearly. It is not all that complicated. Hook the white wire from the AC to the C on the tstat (orange) Other wire from AC/red to the Y terminal on the tstat/yellow wire. Make sure the Y from the tstat/yellow goes to the Y on the board and the C/orange goes to the board on C and that the colors don't get changed mid way from the tstat to the furnace. If they do then you have a HUGE problem and they need to be traced out with an ohmeter.
1 - 16 of 16 Posts