Discussion Starter · #1 ·
I am trying to complete an addition to my home that started 2 years ago. I have gone through 3 electricians on the project and trying to finish the rest myself. I had a circuit breaker that would buzz then trip. I at first thought it was a short, but then put my wulti meter on the wire of that circuit breaker when it was off and I had 120 volts even though the breaker was off. I also had 120 volts on the neutral line for that circuit. Any thought and solutions would be greatly appreciated
 

·
Master Electrician
Joined
·
1,453 Posts
The circuit in question is probably tied into another circuit somewhere, possibly in a receptacle/switch box, etc., in or near your addition.

Start by turning off other breakers until the voltage disappears. Then open the recpt/switch/j-boxes/lights, etc…I’ll bet you’ll find those 2 circuits tied together somewhere.
 

·
Super Moderator
Joined
·
15,650 Posts
Would are you using to detect the voltage? Pen type non-contact detectors can give false positives.
 