I'm getting my furnace replaced and I been hearing about getting it hard wired into a switch instead of an outlet. Some have said its necessary and others have to protect the warranty from the manufacturer. One even said he didnt and kept blowing thermal coupler and he thinks its because of that...Any ideas on this

Thanks
 

· Super Moderator
Joined
·
18,344 Posts
Furnaces are not listed for use with a flexible cord. I have never seen one not hardwired.

A service switch is needed to kill the power while the unit is serviced.
 

· Registered
Joined
·
86 Posts
Discussion Starter · #3 ·
Hard wired

Not anymore mine is over 30 yrs old I know it needs to be piped out of the unit. Then it can be flex with a drip leg...I'm referring to the outlet it generally is plugged into..does that need to be hard wired Into a switch to turn off and on when not in use.
 

· Registered
Joined
·
10,405 Posts
I'm getting my furnace replaced and I been hearing about getting it hard wired into a switch instead of an outlet. Some have said its necessary and others have to protect the warranty from the manufacturer. One even said he didnt and kept blowing thermal coupler and he thinks its because of that...Any ideas on this

Thanks
Blowing the thermocouple has nothing to do with the way the furnace is wired.

Permanent or fixed installations of equipment should not use cords and plugs and receptacles for the electrical connection.

If you wish to power the furnace using a generator connected via extension cord, use a double pole double throw switch for the service switch with the common terminals connected to the furnace lead (hot and neutral) and one traveler terminal group connected to the power feed (hot and neutral). Connect the other traveler terminal group to line going to a male receptacle. The extension cord from the generator is plugged on here.
 

· Registered
Joined
·
86 Posts
Discussion Starter · #7 ·
furnace

yes my furnace is over 30 yrs on and it was plugged in to an outlet. are you saying its required to have a switch?






gold flex coming out of the unit.. now it has to be hard piped in then flex from that point with a drip leg. the reason im asking is Im planning to do this myself..and selling our house and dont want a buyer to have to negotiate against it, however, once I do it what are the chances of a buyer asking for a city inspection vs a home inspection, i just talked with a realtor and she said once they see a new furnace they will ask for a city inspection.. I thought...hmmmm im not soo sure about that. I asked the same realtor if I dont change it out what would the inspector say and she said as long as its functional and running it will pass... hmm to me that kinda contradicts what she said previously. what are your thoughts am I wrong?
 

· Registered
Joined
·
11,194 Posts
I don' know whether it is a local code amendment or perhaps a different definition of furnace. But it is quite common (here) for a central heating (forced air) gas "heater" to come with an appliance cord. They are plugged into a fused outlet. Pull the plug to service the unit.
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
When I was a kid in Vermont, the furnaces in both houses we lived in were plugged into fused receptacle/switch combo devices mounted next to the furnace. I think I remember that from a house in Nebraska when I was much younger, too.
 

· Licensed Electrician
Joined
·
4,352 Posts
Unless there is a local amendment, or the furnace is listed to be cord and plug connected, it is not legal to cord connect a furnace.
 
  • Like
Reactions: Oso954

· Engineer
Joined
·
191 Posts
I've searched on this issue myself in previous years, and there always seems to be an argument between folks in the business. Seems there are inspectors that pass it, and those that won't. I'd venture to guess it's not allowed, but I'm now hearing of areas around the country where it seems to be standard practice (parts of Louisiana, and California are ones I've heard recently.)

When it comes to generator use, I've always thought that a cord and plug solution beats a suicide cord (or any other hack job a homeowner can do.) After all, one of the main reasons homeowners try to backfeed their home is for the furnace.
 

· Registered
Joined
·
7,409 Posts
I don' know whether it is a local code amendment or perhaps a different definition of furnace. But it is quite common (here) for a central heating (forced air) gas "heater" to come with an appliance cord. They are plugged into a fused outlet. Pull the plug to service the unit.
I find that very unlikely. All central funaces need to be hardwired and should have a disconnect at the furnace location. Code does not permit plugging it in. Portable heaters are another story.:yes:
 

· Registered
Joined
·
86 Posts
Discussion Starter · #16 ·
Furnace

I really appreciated everyones input on this..I was going to do this myself..but after weighing out the pro's and con's and my situation,,Im going to let a licensed hvac that can pull a permit do it..because I am selling my house, I figured if I do it.. then a buyer(s) come in and see a new furnace someone is going to want a possible city inspection. That would mean calling someone that has a license and that could be 300-350 and then getting the city out to inspect it because they know your in a bind and that means racking up the charge. If I would stay in this house I most definitely would do it myself along with my neighbor which works in the field.. so you ask why doesnt he do it..well.. he doesnt have the right type of license to get a permit. also he doesnt want to have his name on it after Im gone from here.
There are still sayiong it doesnt need to be hard wire in to that switch.. but I think this guy thats going it will hook it up...

question....if that switch is hooked up will that inspector say anything about it being its connected to the heater when he inspects the mechanical part of it or is it not his area being it's electrical?

thank again
 

· Super Moderator
Joined
·
18,344 Posts
Here are the conditions that allow flexible cord usage.

400.7 Uses Permitted.
(A) Uses.​
Flexible cords and cables shall be used only for
the following:
(1) Pendants
(2) Wiring of luminaires
(3) Connection of portable luminaires, portable and mobile
signs, or appliances
(4) Elevator cables
(5) Wiring of cranes and hoists
(6) Connection of utilization equipment to facilitate frequent
interchange
(7) Prevention of the transmission of noise or vibration
(8) Appliances where the fastening means and mechanical
connections are specifically designed to permit ready removal
for maintenance and repair, and the appliance is
intended or identified for flexible cord connection
(9) Connection of moving parts

(10) Where specifically permitted elsewhere in this
Code

I don't see how a furnace meets the bolded condition.
 