1970s house with aluminum wiring.
Currently in the middle of Alumiconn pigtail installation.
I have a 4 gang switch box that would require 4 alumiconns alone for the ground wire.
Would it be acceptable to place a grounding bus bar in the box? This would take up less space and be less expensive.
Square D terminal ground bars are rated for aluminum wire, and even rated for two wires per port. This would save me a lot of room in the box for grounding purposes.
My question is, is it against code to have a floating ground bus bar in a 4 gang box?