I currently have a 400 amp service with two 200 amp service panels, the ground is a water pipe connected with what looks like 4 awg stranded. There is one rod with 6 awg solid.
If I were to update the grounding system, wouldn't I need to sink rods for each panel?
*Looks like I can install two rods and "tap" to both enclosures-250.62 (D)
Whats the code reference to gas bonding-Never mind, I have it 250.104 (B)
I don't think I will bother the system anyways as there is almost no space outside to sink rods. Just curious what I would do.
What size for the gas bond? It says to size it according to the circuit that is possible to energize it. So since furnaces are hooked up to it and are 15, I would use 14? It would make sense to size it to 12 since 20 amp circuit for the furnace might be installed in the future.
What about flexible gas tubing. Do I have to bond at each connection point or is a bonding the iron gas pipe enough?