New member; first post. Thanks in advance for reading and responding.
Although I’ve read many posts here related to this subject, I’m still confused.
I have a rural property with 200A meter loop on pole. This includes Milbank socket and 200A Siemens load center (W0816B1200CT) w/ 200A main disconnect and feed-through lugs. Of course the neutral and ground are bonded together there and connected to driven ground rod.
Here’s where my confusion begins… I was told by one electrician that from the main to sub-panel(s), I could run triplex URD cable, and then at the sub-panel I could drive another ground and split the neutral and ground there. In other words, I didn’t need to run a separate ground wire from the main to the sub-panel. Several posts here (and a guy at the big box) however, seem to indicate that a separate ground must be run from the main to any sub-panel in addition to the phase conductors and neutral. Which is correct?
If I need to run a separate ground, then what AWG? I will be running to 2 separate sub-panels; one using 4/0-4/0-4/0 via the feed-through lugs and another using 1/0-1/0-1/0 via a 100A breaker in the main (or maybe a 2-pole lug kit). I assume the size of the ground wire is proportional to the conductor size, so what size for each run? Also, if I’m running a separate ground, do I need to drive another ground rod at each sub-panel or is the ground back at the main sufficient for everything? What about plumbing or gas lines? Can they just be grounded through the sub-panel back to the ground at the main? Would separate ground wires need to be sheathed or bare? I’ll be burying the cable in 2” or 2.5” PVC.
Although I’ve read many posts here related to this subject, I’m still confused.
I have a rural property with 200A meter loop on pole. This includes Milbank socket and 200A Siemens load center (W0816B1200CT) w/ 200A main disconnect and feed-through lugs. Of course the neutral and ground are bonded together there and connected to driven ground rod.
Here’s where my confusion begins… I was told by one electrician that from the main to sub-panel(s), I could run triplex URD cable, and then at the sub-panel I could drive another ground and split the neutral and ground there. In other words, I didn’t need to run a separate ground wire from the main to the sub-panel. Several posts here (and a guy at the big box) however, seem to indicate that a separate ground must be run from the main to any sub-panel in addition to the phase conductors and neutral. Which is correct?
If I need to run a separate ground, then what AWG? I will be running to 2 separate sub-panels; one using 4/0-4/0-4/0 via the feed-through lugs and another using 1/0-1/0-1/0 via a 100A breaker in the main (or maybe a 2-pole lug kit). I assume the size of the ground wire is proportional to the conductor size, so what size for each run? Also, if I’m running a separate ground, do I need to drive another ground rod at each sub-panel or is the ground back at the main sufficient for everything? What about plumbing or gas lines? Can they just be grounded through the sub-panel back to the ground at the main? Would separate ground wires need to be sheathed or bare? I’ll be burying the cable in 2” or 2.5” PVC.