Having limit circuit issues on Goodman furnace. I have replaced both limit switches and both rollout switches. I get the 4 flashes before the furnace even lights, so it is next to impossible for it to be actually a limit circuit issue unless I am missing something. Filter is clean. Heat exchanger seems fine from match test (if furnace doesnt light in the first place I'm not sure how it could overheat anyway). I am at a loss here! Continuity checks are fine on limit and rollout switches. Pressure switch has also been replaced. With the 4 flashes coming on before the furnace even attempts to ignite, I'm leaning towards the circuit board. Any ideas
 

· Registered
Joined
·
17,832 Posts
Ohm out all the limit circuits from the board connectors, if they're closed yet it's giving an error right away it's the board or the connection to the board.
 

· Registered
Joined
·
4 Posts
Discussion Starter · #6 ·
I replaced both limit switches. The one at the fire box and the one near the blower. Ohms reading for switches are around 1 to 1.5. I have not checked the wires for continuity, but will try that also! Thanks for the help.
 