I just moved into a home built in 2006 with a Goodman CHPF4860D6AA furnace. All worked fine during the first month, but as luck would have it she no longer fires up and provides the heat we so much love this time of year.

Here's what I know so far:
  • When the thermostat kicks on, the inducer turns on and I feel air blowing to the burners.
  • I never hear the 'click', telling me the gas is flowing. I also don't smell any gas. (The gas water heater and gas stove are working normally).
  • The ignitor never starts, or at least it never starts to glow like other furnaces I've seen.
  • I attempted to light the burners with a lighter, but there was no gas to light.
  • The inducer doesn't ever seem to stop. I was expecting it to shut off after a few failed attempts, but I hung around in the attic for at least 5 minutes and it never shut off.
  • The blower turns on and off as expected when switching the thermostat to Fan only.

After much searching online, I've come to the conclusion that I may have a faulty control board, but wanted to make sure I didn't overlook something simple before calling a professional. Before giving up my DIY card, what other things should I test to help identify the problem?

Thanks!
 

· Registered
Joined
·
15,740 Posts
There's a couple of safety switches next to the board. (the round things with 2 wires on them) Check for voltage across them, if near 0, then with one probe on one wire, touch the other probe to ground. Report your findings.

You'll need a DMM in voltage AC mode.

Sent from my SM-G870W using Tapatalk
 

· Registered
Joined
·
4 Posts
Discussion Starter · #7 ·
I was finally able to find my DVM after digging through the remaining unpacked boxes from the move. Thanks for your patience.

  1. The leads on the gas valve measure zero volts.
  2. The safety switch nearest the gas valve shows 0 volts when attaching leads to both sides of the switch. However, when grounding one lead, each side of the switch measures 27 volts.
  3. The safety switch mounted on the blower housing reads zero volts in all tests.
  4. The board is now flashing 3 times.
 

· Registered
Joined
·
4 Posts
Discussion Starter · #9 ·
"Three flashes indicate pressure switch is not closed, but the induced draft blower is operating."

I checked the hose between the pressure switch and inducer, but it's clean and not-pinched.
 

· Registered
Joined
·
142 Posts
Pull the inducer motor and check it. I had something similar and found a dead bird in the motor of a York Furnace. The bird kept the fan from spinning, but the motor was running.. Could also be a blockage in the venting.
 