Hi, my goodman ac is not cooling. THe suction and head pressure were both about 120. When i put refrigerant in my suction line it barely registers in my liquid line and vise versa. Am i supposed to put refrigerant in both lines? or just the suction. I am using vapor not liquid when charging. Could it be my metering device? :sweatdrop:
 

· Registered
Joined
·
17,837 Posts
First thing -> see if the compressor is actually running. If you have a clamp ammeter, check the draw on the common wire going between compressor and contactor.

If it is running and the pressures remain equal, there's a mechanical failure. Even with no metering device, there would still be a pressure difference produced by the compressor pumping refrigerant around.

-------
answers to other questions:
Just suction with the machine on.

410a has to come out of the cylinder as a liquid and be flashed into a gas, as it's a blend.
r22 is one component and can come out of the cylinder as vapor.

hoses must be purged before adding or air gets into the system.

120 psi standing pressure leads me to believe it's a r22 unit unless it's cold outside.

Remember that if it's low on refrigerant, there's a leak and the solution isn't just to top it off.
 

· Registered
Joined
·
4 Posts
Discussion Starter · #5 · (Edited)
yes it is an r22. the leak was in the schrader and i fixed it. it got low and the lines got real hot, but i cant get it back up. when i put refrigerant in the suction side goes up but it take forever for it to register on the liquid line. is that normal?
 

· Registered
Joined
·
17,837 Posts
yes it is an r22. the leak was in the schrader and i fixed it. it got low and the lines got real hot, but i cant get it back up. when i put refrigerant in the suction side goes up but it take forever for it to register on the liquid line. is that normal?
this is not the time to try adding refrigerant. to add refrigerant, the suction pressure has to be below the pressure in the tank.

the standing pressure is determined by temperature. 120 psi r22 = 69F - what's the temperature outside?

the compressor likely isn't pumping properly if at all. is this a heatpump?

It's never done through the high side with the machine running, it may be best to study up on the theory a bit more or just call a tech.
 