Hello: Hoping for a bit of help/advice on this issue.
I installed a sub-panel in my garage, containing 3 ea 20amp GFI breakers.
The main panel is directly behind the sub-panel so the run between the two is very short and connected via EMT.
The house is in California and was build in the early 1960s. In the main panel, earth ground and neutral wires are all connected to a common bar.
For the sub-panel, I ran a L1, L2, neutral and ground wires. I connected neutral and ground to the common bar in the main panel and the common bar in the sub-panel.
In the sub-panel, I did not bind the bar to the panel (it's still isolated), however, since the main panel has a common bar and that IS bound to the panel, the EMT connecting the two panels will obviously carry earth ground and neutral to the new panel box.
From the sub-panel, I have run EMT and pulled hot and neutral wires that are connected to non-GFI outlets. I am letting the EMT carry the ground.
The problem: As soon as ANY load it placed on any of the circuits the GFI breaker trips. Right now, I simply have the neutral wire from the GFI breaker disconnected and it works just fine, but obviously without the GFI value.
Thoughts?
I installed a sub-panel in my garage, containing 3 ea 20amp GFI breakers.
The main panel is directly behind the sub-panel so the run between the two is very short and connected via EMT.
The house is in California and was build in the early 1960s. In the main panel, earth ground and neutral wires are all connected to a common bar.
For the sub-panel, I ran a L1, L2, neutral and ground wires. I connected neutral and ground to the common bar in the main panel and the common bar in the sub-panel.
In the sub-panel, I did not bind the bar to the panel (it's still isolated), however, since the main panel has a common bar and that IS bound to the panel, the EMT connecting the two panels will obviously carry earth ground and neutral to the new panel box.
From the sub-panel, I have run EMT and pulled hot and neutral wires that are connected to non-GFI outlets. I am letting the EMT carry the ground.
The problem: As soon as ANY load it placed on any of the circuits the GFI breaker trips. Right now, I simply have the neutral wire from the GFI breaker disconnected and it works just fine, but obviously without the GFI value.
Thoughts?