I have two issues I'm curious about.

We just bought a house that was built in 1968 with a two-wire electrical system. A previous owner had replaced maybe half of the outlets with three prong outlets, but didn't ground them. In a couple places, like the kitchen and bathroom, they've added an additional wire that is tied into the main ground in the breaker box.

Here's issue #1. We requested that all the ungrounded three prong outlets be connected to ground as part of our repair agreement. The seller agreed, and had a "master electrician" perform the work. When we showed up at the walkthrough, all of the plugs had been replaced with three prong. I didn't have a chance to test them before closing and assumed the work had been done correctly. This week I finally had a chance to start mapping my circuits and I noticed that everything is still ungrounded (using an outlet tester). What he did was add a GFCI outlet (still ungrounded) to each circuit. I've found some information online that says this is an easy solution for providing additional safety, but it still leaves me without an equipment ground. I'm a little pissed right now, but before I start making calls, do any of you have any experience with this technique? Is it up to code on any level, or is it a cheap/lazy hack? FWIW, I checked my town's website and regrounding requires a permit, but changing outlets does not. I wonder if he did the job this way just to fly under the radar.

I'm not sure how I'm going to pursue this yet, since I signed the document at closing saying the repairs were complete. But I want to make sure I know what's going on before I get too worked up.

And issue #2. Another repair that we had done was to upgrade the house from 100A to 200A service. The same guy did the work, but the only complaint I have there is that none of the circuits were labeled. No big deal, but this is why I'm mapping my circuits. I used a Klein Tools ET300 Digital Circuit Breaker Finder, and came across an interesting problem. The "bathroom" circuit (position #9 in the photo) has a GFCI breaker. However the Circuit Breaker Finder beeps it out at position #5. 5 is a separate but adjacent (in the house) circuit. The outlets on #5 also beep out to 5. I verified each circuit is separate by flipping the switch. So according to this instrument, I have two circuits that beep to the same breaker, and nothing beeps on the GFCI. Is this a common error with this type of instrument, or is there something weird going on with my wiring?



Thanks for your help. I am a first time home owner, and I'm having a blast figuring all this stuff out.
 

·
Super Moderator
Joined
·
16,917 Posts
Adding GFI protection and switching to 3 prong receptacles is a code acceptable method to allow the 3 prong on an ungrounded wiring method. It does not provide a ground. The receptacles should have been labeled "No Equipment Ground".

The directory not identifying the circuits is a code violation.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
I have two issues I'm curious about.

We just bought a house that was built in 1968 with a two-wire electrical system. A previous owner had replaced maybe half of the outlets with three prong outlets, but didn't ground them. In a couple places, like the kitchen and bathroom, they've added an additional wire that is tied into the main ground in the breaker box.

Here's issue #1. We requested that all the ungrounded three prong outlets be connected to ground as part of our repair agreement. The seller agreed, and had a "master electrician" perform the work. When we showed up at the walkthrough, all of the plugs had been replaced with three prong. I didn't have a chance to test them before closing and assumed the work had been done correctly. This week I finally had a chance to start mapping my circuits and I noticed that everything is still ungrounded (using an outlet tester). What he did was add a GFCI outlet (still ungrounded) to each circuit. I've found some information online that says this is an easy solution for providing additional safety, but it still leaves me without an equipment ground. I'm a little pissed right now, but before I start making calls, do any of you have any experience with this technique? Is it up to code on any level, or is it a cheap/lazy hack? FWIW, I checked my town's website and regrounding requires a permit, but changing outlets does not. I wonder if he did the job this way just to fly under the radar.

I'm not sure how I'm going to pursue this yet, since I signed the document at closing saying the repairs were complete. But I want to make sure I know what's going on before I get too worked up.

And issue #2. Another repair that we had done was to upgrade the house from 100A to 200A service. The same guy did the work, but the only complaint I have there is that none of the circuits were labeled. No big deal, but this is why I'm mapping my circuits. I used a Klein Tools ET300 Digital Circuit Breaker Finder, and came across an interesting problem. The "bathroom" circuit (position #9 in the photo) has a GFCI breaker. However the Circuit Breaker Finder beeps it out at position #5. 5 is a separate but adjacent (in the house) circuit. The outlets on #5 also beep out to 5. I verified each circuit is separate by flipping the switch. So according to this instrument, I have two circuits that beep to the same breaker, and nothing beeps on the GFCI. Is this a common error with this type of instrument, or is there something weird going on with my wiring?

Thanks for your help. I am a first time home owner, and I'm having a blast figuring all this stuff out.
IMO you got what you paid for. You had this work done as a condition to buy the house. Of course it is going to get done as cheaply as possible. And to be honest the 200A UPGRADE was NOT a repair, but just that, a free upgrade.
So you got a simple fix and a FREE 200A upgrade out of the deal. I'd say you are ahead of the game.

The GFI load side for non-grounding receptacles is the easiest and generally the most used fix for this situation. Running new wires, or even just a ground wire, is NOT a reasonable request IMO. That is basically a complete re-wire job.
I must say, I find it odd that a 1968 home is wired without a ground. I bet the wiring method in place does have a ground.
 

·
Licensed Electrician
Joined
·
4,352 Posts
I'd be curious to see a picture of this whole panel.

My first thought is that there is no way a permit was pulled for the work requested. No labeling and tandems installed, something is not right. There should be no need for tandems on a 100 to 200A upgrade.
 

·
Registered
Joined
·
47 Posts
Discussion Starter · #6 · (Edited)
Ask, and ye shall receive...

Here is the whole box (minus the front panel):



...and the cables coming in the top. The newer wires (romex?) on the left and far right go to the basement circuits, and are grounded. The house circuits are the silvery braid on the right (Hatfield Hatflex 14/2 NM). I don't think it's a metallic sheath.



I can provide more detail in any particular area too. These images are shrunk down pretty far per the forum rules.
 

·
Licensed Electrician
Joined
·
4,352 Posts
Interesting...I have never seen a 200A panel with so few spaces and IMO, this is not a new panel. I'm not saying its used per se, but I don't think this was purchased within the last 5 years (possibly 10).

I see some minor issues, such as white conductors used as hots but not re identified and the part about no labels, but other than that, I really don't see much to be concerned with.

I also see grounded branch circuits. What prompted you to request for the outlets to be grounded?
 
  • Like
Reactions: NJMarine

·
Registered
Joined
·
47 Posts
Discussion Starter · #8 ·
This is fascinating. Thanks.

The box is a Murray LC2040B1200, and there's a 2010 copyright sticker on the door. But maybe it's an older design or something. I really thought I would get more expansion room too, my pictures don't even show the 6 inches of dead space below the main switch.

The white wires...

The first one on the left from the top is a 60A double pole for the heat pump, the second one on the left is two single pole 30A breakers with a clip between them for the heat pump outdoor unit. The top right is a 30A double pole for the water heater, and the lower right is that GCFI I was talking about.

The grounded branches are all basement circuits. The main living area is ungrounded except for the outlets next to sinks which have a separate ground wire installed. Mainly I'm concerned for my electronics, appliances and anything else I plug into a surge protector. I also didn't like having that many three prong outlets installed with improper wiring.
 

·
Licensed Electrician
Joined
·
4,352 Posts
I apologize for the bad information on the panel's age. It looked to be an old Sieman's panel. I would check into if a permit was pulled for the service upgrade.
 

·
Registered
Joined
·
47 Posts
Discussion Starter · #14 ·
I apologize for the bad information on the panel's age. It looked to be an old Sieman's panel. I would check into if a permit was pulled for the service upgrade.
Actually you might not be that far off. I did a quick google search and I think Siemens owns Murray. Maybe they dumped their old designs under a different brand name.
 

·
Super Moderator
Joined
·
16,917 Posts
I didn't say it wasn't to code.Just stated I didn't like it. Keep the neutrals where they were designed and the grounds go to the added ground buss.
A ground bar does not need to be added to a service panel.
 
  • Like
Reactions: NJMarine

·
Electrical Contractor
Joined
·
1,994 Posts
Depends on the price of the upgrade if it was an very inexpensive upgrade then you got what you paid for but if you paid a large amount I would expect a 40 space panel for room to expand in the future. And possibly arc faults depending on your code cycle.
 

·
Registered
Joined
·
10,018 Posts
Ground fault circuit interrupters provide almost perfect protection against electrocution but does not protect equipment from power surges (power line overvoltage irregularities).

Proper grounding of branch circuits provides some added protection to plugged in equipment in case of a lightning strike and makes possible the use of surge protectors for electronics, and in the absence of GFCI units provides a small amount of protection against electrocution.
 

·
Registered
Joined
·
8,295 Posts
Here's issue #1. We requested that all the ungrounded three prong outlets be connected to ground as part of our repair agreement. ... What he did was add a GFCI outlet (still ungrounded) to each circuit. ...Is it up to code on any level, or is it a cheap/lazy hack?
I'm not sure why you're getting the technical answers to your questions, but not the practical answers.

You got ripped off. It probably doesn't matter if you signed anything, you obviously didn't get what you asked for. This is essentially a legal matter now and up to you how you want to pursue it. Personally I'd definitely pursue it.

Is it up to code on any level? Well, yeah, assuming the GFCI have been installed properly, they will meet code as outlets. However, they are not marked "No Ground", therefore they're not completely up to code. Of course they would not label them such, because then you'd know they're not grounded.

Is it a cheap/lazy hack? I don't think so. It's just something different. Depends on the electrician's/previous owner's intent, which you can't know. But you did get ripped off. Ground and GFCI are each safe in their own way, but they each protect against different things, and they can't cover for each other (i.e. grounding doesn't help with GFCI issues, and GFCI doesn't help with grounding issues.)
 

·
Registered
Joined
·
8,295 Posts
Ground fault circuit interrupters provide almost perfect protection against electrocution...
It does not. It provides almost perfect protection against only specific causes of electrocution. For example, if a child takes 2 butter knives and sticks one in each hole of a GFCI receptacle, the child is not protected in any way. As far as the receptacle is concerned, the child is an appliance operating correctly and will let the current flow.

Of course, proper grounding won't help this situation either....
 

·
Registered
Joined
·
9 Posts
Converting 2-prong outlets to 3-prong

I have read several posts, on this web site about changing 2-prong receptacles to 3-prong receptacles. I am still confused if I can safely do the following: My daughter's recently purchased 1952 home with BX cable (2 conductor) wired (with steel boxes) has all 2-prong receptacles, except in the kitchen where there are GFCIs. With each 2-prong outlet, if I first determine that I have a proper ground between the hot conductor and steel box (by using a 100w incandescent bulb as my tester). Then next, if I affix a ground wire pigtail to the back of the steel box and to the new 3-prong receptacle ground screw, will this serve as a proper and safe grounded 3-prong receptacle?
 