I have a GFCI that wont reset. I did the following.
1. Replaced it, but still trips
2. Removed the load receptacles, but still trips
3. Checked voltage from hot to neutral. 118
4. checked Voltage from hot to ground. 118
5 turned circuit off at breaker box and check for continuity.
6. no continuity at hot to either ground or neutral
7. continuity at neutral and ground
8. With circuit breaker on, I touch my red lead to the hot, but did not touch the black lead to anything and I got 11.5V. (See Attachment)
Any ideas what could be wrong
1. Replaced it, but still trips
2. Removed the load receptacles, but still trips
3. Checked voltage from hot to neutral. 118
4. checked Voltage from hot to ground. 118
5 turned circuit off at breaker box and check for continuity.
6. no continuity at hot to either ground or neutral
7. continuity at neutral and ground
8. With circuit breaker on, I touch my red lead to the hot, but did not touch the black lead to anything and I got 11.5V. (See Attachment)
Any ideas what could be wrong