Buy the 15 amp version and it will work with a 15 or 20 amp circuit


Sent from my Moto E (4) Plus using Tapatalk
 
  • Like
Reactions: HTFreak

·
Registered
Joined
·
207 Posts
If you can verify that the entire crt.was run in 12/2 Romex yes,but if not use a 15A .the GFI is just a different with a night light .
If you can't verify and you install it you run the chance of a burn out along that crt.

Sent from my SAMSUNG-SM-G930A using Tapatalk
 

·
A "Handy Husband"
Joined
·
14,122 Posts
I’m not hear to argue about it. If you like it, fine.
Not being argumentive but if you fail an install, you would need to cite the reason for the failure.
It is often stated on this forum that NM cable cannot be left exposed, but a valid reason is never cited.
Sent from my RCT6A03W13E using Tapatalk
 

·
Super Moderator
Joined
·
16,920 Posts
The NEC allows NM to be run on the surface and where not subject to physical damage. I don't see an issue that would subject the cable to damage.
 

·
Registered
Joined
·
363 Posts
It’s in a garage. Probably around 4’ AFF (it looks like). How is that not subject to damage. I’m sure this is interpretive, but all is needed is a male adaptor at the top and a short nipple in between to be compliant.
 