You need 18" of cover over conduit, 24" of cover over direct burial.
I wouldn't bother with GFCI protecting the entire shed. Just breaker it 90A and G2G.
On the shed, you'll need to GFCI protect the 120V receptacles through a GFCI breaker, deadfront, switch, switch-recep combo, or recep.
The lights do not need GFCI protection and should be on a different circuit from things like saws. Their own circuit is just a good idea. Panel spaces are cheap and you have plenty I'm sure.
You'll need to GFCI protect the compressor once NEC 2020 lands in your jurisdiction. Pull the permit now lol. You can sidestep the GFCI requirement by hardwiring it (is it going anywhere?