I'm installing a generator 6 circut manual transfer switch. Looks like I need to either splice the circuts in the load center (circut breaker box) and bring the wires out to the transfer switch, or I can pull the wires out of the load center and add junction boxes and then route the circuts to the new generator transfer switch.
I have the room in the load center. I'd prefer this method. Is it up to code?
 

· Registered
Joined
·
10,404 Posts
Doing all the splicing in the load center is topologically equal to using the load center as a pass through. This is not permitted in some local cities' code.

With that many (six) circuits, the load center would be much cleaner if you withdraw the circuit cables in question from the load center and use a separate junction box.
 

· Registered
Joined
·
10,404 Posts
Get a 59 cubic inch box for 12 gauge wiring (52 ci for all 14 gauge).

Be sure there are enough holes for the various cables going in. Usually one hole (with appropriate clamp) can admit two Romex cables.

Connect each circuit neutral only to the neutral that accompanies the corresponding hot wire going to a switch.

Connect all ground wires together in the junction box. You can group the ground wires into bundles with jumper wires (pigtails) connecting the bundles.
 

· Super Moderator
Joined
·
18,336 Posts
Typically the NM clamps are for 2 flat cables like 14-2, but only one 3 wire like 14-3. Check the packaging.
 