Hello, I have a GE SunSmart 15312 3-way installation challenge and need help connecting the wires correctly.

I would like to install the GE swith in the upstairs part of a 3-way setup.

Upstairs has two(2) cables - Cable-1 W/Black and White Wires, Cable-2 W/Black, White, Red, Green Wires.

The White from cable-1 is connected to the Black from Cable-2.

The existing upstairs 3-way switch is wired as follows: Cable-1 Black to Common, Cable-2 White to terminal, Red to terminal, Green to Gound.

The downstairs has 1 cable W/Black, White, Red, Green wires; wired Black to Common, White to terminal, Red to terminal, Green to Ground.

What is the correct connection of the Black, White, Red, Blue wires from the GE 15312 to the cables/wires in the upstairs box? Help...

Rob
 

·
Super Moderator
Joined
·
8,858 Posts
You can't use it in the upstairs box because you do not have a neutral wire.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #3
Thanks for the reply jbfan. Would you be so kind as to explain how then to install the GE switch in the downstairs box?
Rob
 

·
Super Moderator
Joined
·
8,858 Posts
Unfortunately, you have the same situation in the downstairs box also.
 

·
Master Electrician
Joined
·
1,165 Posts
nothing like kicking a guy while he's down lol.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #8
Thank you all for your replies and input. Will I have this issue with any 3-way timer or is there one you might know of that bypasses this issue?

Rob
 

·
Registered
Joined
·
2,786 Posts
Thank you all for your replies and input. Will I have this issue with any 3-way timer or is there one you might know of that bypasses this issue?

Rob
If you do not want to fish a another cable that includes a neutral to the switch location, You need to find a 3-way timer that does not need a neutral wire which may be hard to find
 