Hi guys,
Furnace is an American Standard mod# aud080c936j0
Problem: Furnace diagnostic light flashes fast (asking for heat).
Inducer comes on.
igniter does not come on.
Furnace repeats sequence 3 times and then enters lock out mode.
What I tested when the unit was calling for heat:
I have 28 volts to both terminals of both limit switches.
I have 28 volts to all 3 terminals of the pressure switch.
Tested continuity of the igniter and it was good.
I am thinking the board is bad. Am I missing somthing else I should check? Does the igniter have to fall under a certain resistance to function? (I only tested continuity). Thanks for the help.