Hey I have a carrier package unit (model - 48gs-030060301), The furnace will spark and pilot will lite. A few seconds later the burners will fire. Blower kicks on and Furnace runs about 1 minute then shuts off on a roll out fault. I dont think it is a bad switch because I can see the flame (kick back) just before she shuts off.

What would make a (sloppy) flame? It is very sloppy even while it is running. I only seen a straight flame that goes into the exchanger before now. Only about 60% of this flame is going into the exchanger, the other 40% is all missing the ports to the exchanger high. It is almost like it is to much gas pressure, but I could not find the port to measure the pressure.

I did find a burn spot on the control board but it doesn't look that bad and looks like it has been there for some time.

What can I check first and how can I tell for sure if I have a cracked heat exchanger?

Thanks for the help
 

·
Registered
Joined
·
60 Posts
Discussion Starter #2
Hey I have a carrier package unit (model - 48gs-030060301), The furnace will spark and pilot will lite. A few seconds later the burners will fire. Blower kicks on and Furnace runs about 1 minute then shuts off on a roll out fault. I dont think it is a bad switch because I can see the flame (kick back) just before she shuts off.

What would make a (sloppy) flame? It is very sloppy even while it is running. I only seen a straight flame that goes into the exchanger before now. Only about 60% of this flame is going into the exchanger, the other 40% is missing the ports to the exchanger high. It is almost like it is to much gas pressure, but I could not find the port to measure the pressure.

I did find a burn spot on the control board but it doesn't look that bad and looks like it has been there for some time.

What can I check first and how can I tell for sure if I have a cracked heat exchanger?

Thanks for the help
 

·
Registered
Joined
·
1,796 Posts
If the flame is "kicking back" and tripping the roll out switch then an exchanger fault is quite possible. If this "kicking back" back occurs as soon as the fan blower turns on then it's likely.
You can pull the burners and scope with a camera, check the hot air plenum before the blower comes on for CO but most likely it will be more cost effective to get a tech in with the right equipment and the knowledge of how to use it.
Overgassing is possible and that can be explored with either a manometer or the clocking of the meter.
 

·
Registered
Joined
·
4,494 Posts
Watch the flame before the blower starts. If the blower starts and the flame starts to dance it is one indicator of a cracked exchanger....but start there.
 

·
Registered
Joined
·
60 Posts
Discussion Starter #5 (Edited)
No it is all over the place before, the fan even comes on. what would cause that? Im not sure how I missed the plug to test pressure, but I think I may need to check pressure.
 

·
Registered
Joined
·
60 Posts
Discussion Starter #6
Im not sure why this thread is in here twice but . . . When the flame first comes on it is all over the place, before the fan starts. That would make me think it is not a heat exchanger. What could make it all over the place from the time the flame comes on.

Thanks for the help.
 

·
Hvac Pro
Joined
·
23,038 Posts
Heat exchanger is probably partially plugged with rust or soot and that is from bad combustion which may be related to the cracked heat exchanger. Should get it properly checked by a Pro.
 

·
Registered
Joined
·
60 Posts
Discussion Starter #8
okay new update the flame is all over the place before the fan comes on, but yes when the fan comes on it blows it out the flame.
I did take an inspection camera and shove it up the exchanger and did not see a crack, I opened up the shell and looked all around each side of the heat exchanger except for the side facing the fan and still nothing.

does that mean it is the exchanger? i just don'twant to buy another one of i don't need it.





thanks again for all the great help
 

·
Registered
Joined
·
1,662 Posts
Doed this unt have an induce draft blower? Sounds like a clogged exaust, however, if it has an induced draft blower it should not start if the pressure switch is working properly.
 

·
Registered
Joined
·
2,362 Posts
Those heat exchangers are good at rusting up. Open the access cover so you can see the tubes and look for rust on the seams. Push on the rust spot with your fingernail and it will go right through most of the time.

When the flames can't make it through an exchanger the carbon monoxide goes from a few parts per million to several thousand ppm so don't be breathing any fumes. Ten thousand ppm will kill you in under 2 minutes.
 

·
Registered
Joined
·
60 Posts
Discussion Starter #12
Doed this unt have an induce draft blower? Sounds like a clogged exaust, however, if it has an induced draft blower it should not start if the pressure switch is working properly.
Yes it does have a draft blowe, and I didn't think to check it because I could hear it, and if it wasn't working it should start, right? That is what I thought as well. It seems there is enough pressure for the pressure switch but not enough for the flame. When I feel around the side of the unit there is no air coming out of the draft vent. I am going to head back out tomorrow and check the blades I bet they are rusted or gone.

But still that would not explain why the flame is all over the place, but once again once the blower starts the flame goes out. Has to be a cracked exchanger as well, right?
 

·
Registered
Joined
·
1,796 Posts
An ID that continues to cause a flame rollout would also require a pressure switch to work with a coresponding lower pressure drop than what it's designed for. A PS always become less sensitive or fails. I've never seen one become more sensitive than what it's designed for.
The burner problem can occur from being overgassed or the burner diffusers being debris filled but the timing of the flames being affected by the main blower coming on just says you have a real big crack in the exchanger.
 

·
Retired Moderator
Joined
·
25,769 Posts
New member---please don't start duplicate threads on the same subject---I merger two threads of yours---

Moderator
 

·
Registered
Joined
·
60 Posts
Discussion Starter #17
update - I just spent about an hour looking for a crack in the exchanger. I pulled out the blower so I could get my upper body in there to look. I could see 99% of the exchanger and used my inspection camera for what I count not see.

I can not find a crack, I did find the blades to the draft fan all over the place. So I know I need to change that. but my question is would you change the whole draft assembly or just the blades. I did not spent a lot of time on the fan but it looks like I have to pull out the board and the burners and everything.

Has anyone ever worked on this model before 48gs-030060301
 

·
Registered
Joined
·
624 Posts
The squirrel cage on the inducer rusts and falls apart on those units.
It doesn't have a pressure switch. It is one of those centrifugal switches.
It is satisfied as long as the motor spins and will not know the squirrel cage is practically gone. The roll out switch catches that.

You can remove two 5/16 inch screws on the 90 degree elbow on the unit to see the squirrel cage. Checking the heat exchanger before replacing the inducer (if it is that) wouldn't be a bad idea though...
 

·
Registered
Joined
·
23 Posts
No all Carriers use a 3 wire pilot switch that fails regularly

The middle wire is the 24v hot leg and the other 2 are HOT or COLD
this is a flame sensor like the mercury flame sensors we used to have but Carrer uses a bimetal that expands/contracts to switch from spark ignition to main burners and gas valve. very common. the induced draft provbing switch will also be suspect as will the pressure switches tubings orifices upon which it connects.
 