During hurricane Irene last year my basement flooded (about 1 foot if water) and caused danger to my furnace. I realized that all that seemed to be damaged was the circuit board. So I went online ( I am a total novice ) and googles the issue and found I could buy and replace it myself. I did and it seemed to work. The only issue I have is sometimes it won't go on until I literally hit the furnace no to hardly and then it goes on. What could be the issue? I attached a YouTube video of the issue as well.

http://youtu.be/KAPrO4EXlrw

http://youtu.be/KAPrO4EXlrw
 

· Registered
Joined
·
1,796 Posts
Something electrical is loose. Thermostat connections inside the furnace/ door switch/ etc.
I would check over the connections on your board since you've just changed it.

Another question I have is do you have enough room in front of the furnace to ever change the blower motor?
 

· Registered
Joined
·
9 Posts
Discussion Starter · #4 ·
Furnace wont start up unless hit.

During hurricane Irene last year my basement flooded (about 1 foot if water) and caused danger to my furnace. I realized that all that seemed to be damaged was the circuit board. So I went online ( I am a total novice ) and googles the issue and found I could buy and replace it myself. I did and it seemed to work. The only issue I have is sometimes it won't go on until I http://youtu.be/KAPrO4EXlrwliterally hit the furnace no to hardly and then it goes on. What could be the issue? I attached a YouTube video of the issue as well.
 

· Super Moderator
Joined
·
11,055 Posts
I say a loose connection.
You are not hitting that thing hard enouogh to move anything inside, but the wires may be close to where you tap it.
 

· Registered
Joined
·
1,407 Posts
Turn off the Tstat and jumper R-W on the furnace.

Sent from my iPhone using DIY Forum
 

· Registered
Joined
·
1,407 Posts
Jjboy... I can turn off the thermostat but what do you means by the r-w??
The control board you installed. There are the low voltage wires connections coming from the thermostat. If you turn off the thermostat and jumper R-W at the control board, the furnace will turn on. You can check if the loose connection is inside of the furnace or the thermostat wires.
 

· Registered
Joined
·
69 Posts
I had a new carrier furnace installed and it did the same thing, had to wake up in the middle of the night and hit the darn thing, the service guy never figured it out because it always worked when he came to the house,turns out is was the switch on the door, I just shorted it out, problem solved.
 

· Registered
Joined
·
37,499 Posts
Was that salt water that got in?
I would have replace the whole unit. Keep an eye on it, I'm betting the whole bottom area that was under water is going to rust out.
 

· Registered
Joined
·
1,662 Posts
It is posible that that switch is not opening when the unit shuts down. A furnace in one of my houses has something on the control board that looks for that switch to be in the open position before it will start the Induced draft blower. It is a safety feature to keep someone from jumpering the pressure switch.
 

· Registered
Joined
·
9 Posts
Discussion Starter · #19 ·
danpik said:
It is posible that that switch is not opening when the unit shuts down. A furnace in one of my houses has something on the control board that looks for that switch to be in the open position before it will start the Induced draft blower. It is a safety feature to keep someone from jumpering the pressure switch.
So any ideas on fixing it. Does the switch need replacing?
 