We have to turn the circuit breaker off in the summer because the furnace comes on. Has done this with all three thermostats we have used over the last ten years. AC is separate unit on separate thermostat
 

·
Registered
Joined
·
3,493 Posts
Heater on

Sounds like wrong thermostat or wired for cooling.
 

·
Registered
Joined
·
955 Posts
Agree with Sultini. Sounds like the stat was set to cylce air in fan mode at higher temp and someone has wired it to kick on heat instead.
 

·
Registered
Joined
·
3,630 Posts
if the heating stats are all set down to 50F or as low as they can be set you should have no heating during the summer.if the heat starts right off the bat when the cooling starts it is a control mis-wiring.if the heating stats are solid state and set for heat/68F they might be anticipating a call for heat as the cooling drops the temperature within the house
 

·
Registered
Joined
·
3 Posts
Discussion Starter #7
Thanks All;
Furnace is propane. It runs normally during winter. It's on off cycling has no correlation operation of AC which is on separate thermostat and a separate unit.
When it gets up in the eighties in the single wide the furnace will kick on. Not necessarily every time as I have not monitored that yet. There are two wires to the thermostat I think. I have changed it twice from original mercury switch to current programmable thermostat.
I have no recollection of whether this was happening before or started after I replaced motor in furnace six or so years ago.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #8
Heat set in range of 58 to 72 degrees. More likely to come on in high eighties when Air conditioning is off as AC is usually set at about 80 +/- 2*
 