I was under the house dealing with a plumbing issue and I noticed something that didn't look right to me. The home has a crawl space with dirt floor and low clearance. Suspended from the rafters is a Goodman 95% high efficiency furnace. I guess it was installed by the pervious owner and looks fairly new.

The flue pipe looks to be two inch PVC. It rises about three inches over and eight or ten foot run to make it over a beam and then drops about six to eight inches over a ten foot run so it can exit through the skirting.*

I'm not familiar with these high efficiency furnaces. I've never seen PVC used as a flue pipe and I've never seen a flue pipe go up and then down. Should I be concerned?

Greg
 

· Registered
Joined
·
5 Posts
Discussion Starter · #3 ·
Janice,

Thank you for the link, but that rather long article does not answer my question and is not really relevant. That is a large commercial installation of water heaters not a residential installation of a furnace. Yes, they both used PVC, but that really does not matter. All it really tells me is that PVC can be used in some instances for flue gas. Not all that helpful.

Greg
 

· Experienced HVAC Tech
Joined
·
357 Posts
In my area a PVC flue can slope down but only if:

1. The slope is towards the furnace
2. It slopes in to an in line condensate trap which then drains into an approved drain
3. It slopes to the outside to that the condensate will pour outside from the end of the pipe
 

· Registered
Joined
·
5 Posts
Discussion Starter · #6 ·
It slopes back towards the furnace for the first ten feet but ends up in the joist bay to get over the 6x6 horizontal beam that the joists sit on. On other side of the beam the pipe is in the joist bay. Then there two 45 degree elbows to bring the pipe back below the joists and out through the skirting. So the pipe goes up three inches as it travels away from the furnace and then down six or eight inches towards the skirting. Not so much a dip, but a hill.

I've been trying to read about this type of furnace and it seems the slope back to the furnace is so the condensation can be drained. The drain pipe (1/2 inch PVC) feeds into a small pump that pumps the water out the same side of the house but several feet away from the flue pipe.

Greg
 

· Experienced HVAC Tech
Joined
·
357 Posts
Hopefully. But to me the "hill" in the flue pipe slopes down into two allowed locations ( outside and into the furnace) however it is allowed in my local codes. You should also check your local code and what the manufacturer recommends. Some manufacturers don't want the flue pipe sloping down at all other than towards the furnace. Others say its ok to even pipe the flue straight down and then to the side. It all depends
 

· In Loving Memory
Joined
·
42,671 Posts
If your areas temp never drops below 32, you probably will never have a problem with it. Its not within code for that furnace to be ran that way. but, in reality, it won't hurt in mild climate areas.
 

· In Loving Memory
Joined
·
42,671 Posts
A "hill" will not usually cause an issue. A "valley" on the other hand is bad news. PS lockout = Pressure Switch lockout. You furnace will not fire because it doesn't sense correct intake/exhaust flow,