Discussion Starter · #1 ·
I have a gas Rheem furnace model # 80pj07ear01 with central air. My a/c and heater work but my blower will not turn off with the thermostat set on AUTO.

I'm not sure where the blower relay is located to give it a whack or two, is it on the board posted below?


I have also read in anouther post that ''the crossover tubes on the burners were clogged'' which caused the same problem I am having. Not sure how to clean those if thats the problem.







Do I need to replace this?? I found the same model (62-24268-03) on amazon for $98 shipped.

 

·
AKA HVACTECHFW
Joined
·
2,426 Posts
its on the board...... however, first check for 24V from G to C at the board.... this will tell you if it is t-stat or relay in control board.
 

·
Administrator
Joined
·
41,821 Posts
A. Should be the blower relay.
 

·
Registered
Joined
·
7 Posts
Discussion Starter · #10 ·
**Update**

I ordered the board from a amazon seller for $100 and got it in 5-6 days. I just installed it and the unit works great :thumbup:
I checked with a local HVAc supply store and they wanted $225 for the board.
 