If I run my furnace in heat cycle or ac cycle, the fan may run fine to shut off after cycle but sometimes stays on. If I tap the side of the furnace it shuts off. Could this just be the blower motor relay or is it the sequencer. this is a bryant electric furnace.
 

·
Hvac Pro
Joined
·
22,729 Posts
Sequencer only works with the heat. If it stays on with AC then it is the fan relay/blower motor relay.
 

·
Registered
Joined
·
4 Posts
Discussion Starter #3
Thanks yuri, I went to a parts dealer and he recommended that I pull a wire off of the sequencer. He said that if the problem does not happen again that it is the sequencer.
 

·
Hvac Pro
Joined
·
22,729 Posts
Not the best advice. There should be more than 1 sequencer and if you disturb them and yank wires off they sometimes start to stick and you then created a problem. Sequencers don't work with AC.
 

·
Registered
Joined
·
4 Posts
Discussion Starter #5
I can not remember what the wire did but it was a brown one connected to an orange one with terminal clip
 