Fuel oil furnace blower fan

947 Views 1 Reply 2 Participants Last post by  beenthere
Burner and blower fan won t run with out fan limit switch button in the manual position. Button pulled out auto position. Burner won t run
1 - 1 of 2 Posts
Was the fan limit switch recently changed. If so. Sounds like the line wire was put on the fan load terminal, instead of the line terminal.