My house is almost 6 years old and I have a fluorescent light fixture(T12, 2 tubes, 48 inches) in my garage ceiling that recently will not work. I thought maybe the fluorescent lights needed changing and so I replaced them. It worked for a a day or two and now it doesn't work at all. After replacing the old tubes and I first turned the switch on, I could see a small dimmer of light that flicked on at the end of the tube but now it doesn't do it at all. Is it the ballast? the starter? should I replace the whole unit?
 

·
Banned
Joined
·
5,990 Posts
Make sure the bulb is seated properly. Some bulbs have an index mark on the metal end.

If they worked once I assume the fixture is grounded.

It sounds like you should try new starters. You may need a new ballast but a whole new fixture sometimes costs the same [but the new fixture may ask for 90°C wire and you may have 60°C wire].

I guess there is some remote chance it is the sockets [the tombstones] but checking this is difficult.
 

·
Banned
Joined
·
5,990 Posts
FLOURESCENT TROUBLESHOOTING
-blinking or dim: cold drafts hitting lamp
-dim: dirty bulb
-slow starting in high humidity: dirty lamps or low supply voltage
-short lamp or starter or ballast life, lamp won't start: miswired ballast (for a two lamp fixture, both ends of the same lamp must glow when you short the starter connections).
 