1 - 6 of 6 Posts
I'm looking to get backup power to my furnace from a generator but I'm right on space around the furnace. I do have plenty of room about 10' from the furnace at the ceiling.
Is it safe to connect a power cord w a male end directly to the romex wire that comes from the furnace inside a junction box? I know I can install a single outlet on the panel side to plug the power cable into..but I'm not sure about connecting the cable to the romex
Thanks in advance!!!
**Sorry, the title should be power cord and not extension cord**
· Semi-Pro Electro-Geek
It's not code compliant to put a plug on romex, or to use a cord and plug to connect your furnace. You could do it anyway, but it's not to code. The code compliant way to do this would be to install a power inlet (like this: http://www.amazon.com/Leviton-4937-Weatherproof-Wallplate-Receptacle/dp/B00074USHY/) along with a double-throw switch (a regular 3-way works for this) to transfer the furnace from line power to generator power.
(Furnaces using 120 volts only, fed by a single breaker)
Somewhere between the furnace and the breaker panel, along the cable that feeds the furnace --- put a 4 inch square junction box. In the box you put one 3 way switch and a standard (15 amp) male receptacle aka inlet.
Connect the neutrals to the neutral prong of the inlet. Connect the furnace hot wire to the common (dark) terminal of the 3 way switch. Connect the inlet hot terminal to one traveler (bright) terminal of the switch. Connect the hot wire from the panel to the other traveler terminal of the switch.
Use an ordinary but grounded extension cord to connect the inlet to the generator when needed. Flip the switch for generator or utility power as needed.
1 - 6 of 6 Posts
