I am remodeling an old 2 story house, and am installing 4 baths, 2 up and 2 down, 2 above the other 2. I want to install only 1 fan for all 4 baths, in the attic. Is this practical? If so, what size fan and motor should I look for? I'm thinking of venting it thru the roof, before I have the roof redone.
 

· Banned
Joined
·
5,990 Posts
"1.) First find the volume of the bathroom. Volume = length x width x height
2.) Find the CFM (cubic feet per minute). Volume / 7.5
3.) This CFM is the minimum airflow required to achieve 8 air exchanges per hour.

Example: Volume = 10 x 6 x 8 = 480
CFM = 480/7.5 = 64
In this example you would only purchase a fan that has a CFM listed on the box greater than 64."

Ductwork/fitting losses may be significant for this application and if you really want to do it right you need the fan curve.
 

· In Loving Memory
Joined
·
42,671 Posts
Min intermitant bathroom exhaust rate is 50CFM.

4 bathrooms, means you would need a fan capable of 200CFM.
Cost you more to reheat the fresh air, then you sane on fan cost.
 

· Hvac Pro
Joined
·
25,193 Posts
And you can depressurize the house/downdraft the chimney and get CO poisoning. Would need a make up air inlet and that wastes LOTS of energy $$. I removed my central fan and replaced it with an HRV.
 

· Banned
Joined
·
5,990 Posts
I am remodeling an old 2 story house, and am installing 4 baths, 2 up and 2 down, 2 above the other 2. I want to install only 1 fan for all 4 baths, in the attic. Is this practical? If so, what size fan and motor should I look for? I'm thinking of venting it thru the roof, before I have the roof redone.
I guess you should price out all the options in view of the cautions. I s'pose you'd also need to balance the bathroom vents with dampers, just like a miniature HVAC duct system.
And buy a digital readout CO detector.
 

· Registered
Joined
·
2 Posts
Discussion Starter · #7 ·
Thanks a million for the input! It will probably more practical for me to put individual fans in each bath! I can make the vent pipes of the 2 downstairs baths to share an exterior exhaust vent through the outside wall, which is frame, with vinyl siding. The upstairs vents can go into the attic, and share an exhaust vent thru the roof.
 