Is there any way to tell what kind of service (100amp, 150 amp, etc) installed by looking at the gauge of wire coming in, the meter, etc?
-Jeff
Jeff.,
My answer will be yes and no due few factors ,.
• Main breaker size
• Main service entrance conductor size
Is this in the conduit { pipe }
Is this is a SE cable { look like monster sized NM cable }
•Typically 200 amp service will use 4/0 AL or 2/0 CU { 120mm² or 70mm²}
•Typically 150 amp service will use 2/0 AL or 1/0 CU { 70mm² or 55mm²}
•Typically 100 amp service will use #1/0 AL or #2 CU { 55mm² or 35mm²}
Those conductor size will depending on size and distance { some case it will increase due distance }
Merci,Marc