First off, I am new to this forum so I am not sure if this is where I should post this, so please bare with me here.


I have removed an old range that had three wires rather then the new (3) and (4) metal prongs that were attached to the back of my old range. However, my New range has (4) hookups with essentially the same as my original but what appears to be now also a ground wire. My system however in my house is ungrounded.

My question is, would it be OK to utilize my (3) wires that use to be hooked up to my old range to hook up to my new range via the back paneling. Having the White in the Center, the Black to the Black and the last Wire to the other Wire Device & then put then screw the nut in place to ensure the wiring does not get loose?

I also have pictures of this scenario if you can not envision what I am asking and my setup that I am attempting to make vivid via this post.

Feel free to contact me via e-mail @ [email protected]

If you know about this topic and have genuine advice and are qualified please contact me, although if you are not familiar with this sort of setup, electrician type installation please refrain from contacting me as I would like to approach this as professional would.

Also if there are different options as well, please let me know which ones are my best. However, I would like to just hook up the three wires to the back of the range as that would be the easiest for me and the Lowe’s guy said I could do that if I wanted but he suggested in the future to get my system rewired so I had either a (3) prong or (4) prong system, rather then the typical wires that I have resembling those that you twist together when installing a ceiling light or fan for example.

Frigidaire 3011 Series 30-in Freestanding 4-Element 4.2 cu ft



Links to pictures:


Pictures of my current hookup that was utilized to hookup my old range and this is what it looks like after disconnected. Appears to be identical to the new (3) or (4) prong setup, just with Metal pieces on the new Plugs rather then old fashion Wiring



#1: http://i43.tinypic.com/9tl2wz.jpg




#2 http://i41.tinypic.com/35hh0t3.jpg



#3 http://i39.tinypic.com/2wf31jk.jpg




#4 http://i39.tinypic.com/aufiwk.jpg

New Range Back of Paneling that needs to be Hookup with old wires


#5 http://i43.tinypic.com/15zltv.jpg


#6 http://i43.tinypic.com/34pm4g4.jpg



Your help would be appreciated.

Gary



 

·
Super Moderator
Joined
·
9,304 Posts
Welcome from Newnan!

The range you are replacing was not a plug in type, but hard wired, correct?

You are going to hear something you will not like.
The wire from the panel will need to be replaced to meet code.
The current wiring did not meet code then, and is not code now.
I know that most of GA was wired the way yours is now.

You need to run an 8/3 with ground or a 6/3 with ground.
Buy a 4 wire range receptacle and a 4 wire power cord.
 

·
Lic Electrical Inspector
Joined
·
1,843 Posts
Sorry I can't see the pics because of webfiltering. What type of cable is it? Is it romex or SE cable? Describe the conductors of the cable.
 

·
Super Moderator
Joined
·
9,304 Posts
Sorry I can't see the pics because of webfiltering. What type of cable is it? Is it romex or SE cable? Describe the conductors of the cable.
Romex.
 

·
Registered
Joined
·
9 Posts
Discussion Starter · #8 ·
Thanks for your replies, and since you were unable to envision what I was talking about since the filters blocked your ability to see the picture links, I have uploaded them on here.

Hopefully this will give you a better idea of what I am dealing with. The first pictures are of the range wires and box that were connected to my old range and the last picture is of my new range that I need to hook up to.

The Lowe's guy said temporarly I could put the three wires in the back of the New Range and then use a nut on each wire to keep them pressed back. However, he would suggest getting it rewired to be more safe I suppose. I had never had problems with safety on my old range wire with the current wiring system I have, so I am not sure if this approach would work or not? Being just hooking up the three wires to the new range and bolting them on as you would if you had the (3) Prong?
 

·
Licensed Pro
Joined
·
1,571 Posts
Re-read what JB said (post #2). That wiring is not and has never been the proper wiring for a range. You need to run new wires (8/3 or 6/3) back to the panel.
 

·
Remodel and New Build GC
Joined
·
9,927 Posts
Welcome from Newnan!

The range you are replacing was not a plug in type, but hard wired, correct?

You are going to hear something you will not like.
The wire from the panel will need to be replaced to meet code.
The current wiring did not meet code then, and is not code now.
I know that most of GA was wired the way yours is now.

You need to run an 8/3 with ground or a 6/3 with ground.
Buy a 4 wire range receptacle and a 4 wire power cord.
JB..... I know I'm probably dead wrong or just mixed up.... but I thought since we went to 3 wire w/ground for appliances.... we were not required to upgrade the the feed... and we could just ground the appliance with a jumper to neutral.

Could you clarrify and correct me.
 

·
Licensed Pro
Joined
·
1,571 Posts
JB..... I know I'm probably dead wrong or just mixed up.... but I thought since we went to 3 wire w/ground for appliances.... we were not required to upgrade the the feed... and we could just ground the appliance with a jumper to neutral.

Could you clarrify and correct me.
If I may... connecting to an existing 3 wire range or dryer is permitted IF it is wired correctly. The only correct three wire range or dryer circuit is with three insulated conductors or with SE Type cable which originate at the service panel (where neutral and ground are bonded). Two conductor Romex type cable is not and never has been correct.
 

·
Remodel and New Build GC
Joined
·
9,927 Posts
If I may... connecting to an existing 3 wire range or dryer is permitted IF it is wired correctly. The only correct three wire range or dryer circuit is with three insulated conductors or with SE Type cable which originate at the service panel (where neutral and ground are bonded). Two conductor Romex type cable is not and never has been correct.

Thank YA.... I understand, and never saw the original wiring, and thought it was an issue of 3 wire verse 4 wire code upgrading.

Best
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
JB..... I know I'm probably dead wrong or just mixed up.... but I thought since we went to 3 wire w/ground for appliances.... we were not required to upgrade the the feed... and we could just ground the appliance with a jumper to neutral.

Could you clarrify and correct me.
The problem is that the existing cable is two insulated conductors with a bare ground. The old code allowed the use of three INSULATED conductors: two hots and a NEUTRAL, with the frame bonded to the neutral. This bare grounding conductor was never allowed to be re-purposed as a current-carrying neutral.
 

·
Registered
Joined
·
9 Posts
Discussion Starter · #14 ·
Thanks everybody for your advice, it looks like I am going to have to set it up for the proper wiring, as my wires should not be utilized as proposed for properly setting up this system. I probably will contact an electrician out here in GA, but I am hoping to get this job done for a good deal and done correctly.

Any thoughts on how much it would cost to have this installed and have the wiring altered to the two different variations suggested?
 

·
Super Moderator
Joined
·
14,640 Posts
There are too many variables to give an idea on prices.

The wiring will need to be all new, not altered.
 

·
Super Moderator
Joined
·
9,304 Posts
Thanks everybody for your advice, it looks like I am going to have to set it up for the proper wiring, as my wires should not be utilized as proposed for properly setting up this system. I probably will contact an electrician out here in GA, but I am hoping to get this job done for a good deal and done correctly.

Any thoughts on how much it would cost to have this installed and have the wiring altered to the two different variations suggested?
Where are you located?
 
  • Like
Reactions: stickboy1375

·
Registered
Joined
·
9 Posts
Discussion Starter · #19 ·
I attempted to send you a PM, but it said I needed 15 posts to send a PM, so it would not let me. Maybe if you send me a PM it will go through since you probably have over 15 posts.

Gary
 

·
Super Moderator
Joined
·
9,304 Posts
PM sent.
Let me know if you got it.
 