My SquareD panel has room for almost twice as many single breakers than screws on the grounding bar. Putting two ground wires under a single screw not not make for a sturdy connection. What do people do?
 

· Registered
Joined
·
10,408 Posts
An additional grounding bar can be purchased and screwed onto the back of the panel, making sure to have a good electrical contact including scraping the paint off where the new bar touches the panel.
 
  • Like
Reactions: SandyKim

· Registered
Joined
·
775 Posts
The label on the inner door or thereabouts should tell you how to double or even triple lug a grounding wire. Most feel it's good practice to pre twist the conductors although this isn't usually required. The label should also tell you which ground bar kit to get. If not, you can download info based on the product number. Once you find the right GBK and obtain it, follow the instructions included with it. You may need a 10-32 tap
 

· Registered
Joined
·
39 Posts
Discussion Starter · #4 ·
I can't seem to find a grounding bar kit - at least what I would expect it to look like. The panel is SquareD, CAT.ON.QO42M, Series T3B. The grounding bar is actually just screws on the back wall of the panel on both sides of the breakers. What would this grounding bar kit look like?
 