Hello
I live in the northeast. I need to run electrical power to a pond which is 50 ft from the house. There is a shed adjacent to the pond ,but that does not have electrical power.Is PVC conduit the way to go and how deep in the ground shall I lay it. What guage wire should I use and are there any good information or articals I could read. In the past I received some great recommendation.

Thanks
 

·
Registered
Joined
·
774 Posts
PVC is the preferred method. The depth is usually 18" of cover. Sometimes you can go shallower and sometimes you have to go deeper. How many volts/amps and what is the trench going under (ie grass or driveway)
 

·
Registered
Joined
·
5,468 Posts
are there any good information or articles I could read. In the past I received some great recommendation. Thanks
There is plenty of info out there, search on Google,
Or go to Mic Holts forum.

Otherwise tell us more please ?

Expected loads in shed ?
What loads are already on that circuit ?
And the route of the cable ?