I'm troubleshooting an issue at a house and came across the following rather odd circumstances. I pulled in an electrical contractor with 33 years of experience and even he was dumbfounded and had no answers (said he'd consult other electricians). Just seeking ideas from where ever I have access.

-House is a regular ranch home in the US Midwest with a 100AMP service. Off the bat, we measured the power supply as 244V not 240V (I know it fluctuates as you measure it, but in my 10 years of working on houses I've never seen it go outside the 239-241V range).

-The power supply is not balanced for some reason: One leg on this house has 130V and the other 114V. The current on the neutral is much less than the difference between the currents on the two legs. Specific example: leg 1 had 28A and leg 2 had 4A yet the neutral was not 24A (28-4) it was 18A. Then I checked for current on the ground and baam - the ground was carrying about 6A. Yet I can touch the ground and not get shocked! I measure the voltage on the ground and it is 0V. I verified this to be a good earth ground.

-Initial suspicion was that one of the outlets in the house is wired incorrectly with the neutral going to the ground and vice versa but I checked all the ground wires coming to the panel and none were hot.

Anyone ever experienced anything like this? Any ideas? I'm really confused by how the meter was showing 6A on the ground for the service yet no volts?!? How can there be current without voltage? Or is the voltage so low (less than 0.01V) that my meter could not show it?
See less See more
1 - 20 of 28 Posts
Well pump or city water?
Electric water heater with a bad element. Turn the WH breaker off and retest.

If not that turn all breakers off and retest. Turn breakers on 1 at a time until problem gomes back.
The issues I described were found at the breaker panel, not on a specific circuit. These are issues with the entire service to the house.

City water. The house however does not have a cold water ground, just an earth ground (old house, old code, current code requires two grounds, cold water supply and earth).

House has no electric water heater.

I like rjniles' idea, just might try that.
bad meter/meausuremt? v=ir so yes, the voltage cant be zero. what about bad neutral from the house to the pole or somewhere in POCO system....just faulty, not completely bad... so that during a portion of the 60hz wave the neutral is not functional (possibly getting hot at a near broken connection, so resistance shoots up), the ground becomes best path to POCO for that cycle or two, then the neutral cools....etc etc...replayed over many times a second. the meter may not have enough resolution to determine the true RMS voltage if this is happening quickly.... just a guess
I like rjniles' approach. Kill all the breakers and retest. This is a good way to determine where the problem resides (POCO or house.)
Get a different electrical contractor.
  • Like
Reactions: 2
The issues I described were found at the breaker panel, not on a specific circuit. These are issues with the entire service to the house.

City water. The house however does not have a cold water ground, just an earth ground (old house, old code, current code requires two grounds, cold water supply and earth).

House has no electric water heater.

I like rjniles' idea, just might try that.
Bad utility neutral in your service drop to the weather head. Go outside and look at the neutral from the weather head to the transformer and look for broken strands. Your neutral will look like a wire rope. Have you been noticing any dimming and brighting with your lights?
  • Like
Reactions: 2
I would also turn all the breakers off including the main and slowly turn on breakers till you get the voltage. If you get it without the main on then something is happening between your panel and the weather head.

Edit:

I have seen as high as 127 on one leg here. Usually hangs around 120-125 though.
You will not get any voltage measurement on the ground or the neutral legs, because they are at earth ground potiental, even if there is power flowing onto these legs. The amperage you are seeing is flowing from the hot legs, through the loads and then onto the ground and neutral legs, thus indicating on your meter. The voltage difference you are seeing may be the result of there being different loads on the different legs. More load could be causing a voltage drop. Use RJNiles approach, and turn off all the breakers, measure the voltage at the two hot legs coming in, and then start from there. IF the voltage is till not balanced with no load on at the house, contact the power company to repair the transformer. If you do get balanced voltage, proceed to the next step and turn on each individual circuit while measuring voltage and current to see when the problems develop
See less See more
Get a different electrician. The voltage imbalance between the service legs is a clear indication of a bad service neutral connection. The current on the ground conductor is another symptom of that. Current on the water pipe bonding wire is normal if you have city water with metal piping between houses - some current will return to the utility through your neighbor's water piping, which is fine. However, any current on the grounding ELECTRODE conductors (wire to ground rods or slab rebar) is always abnormal and often indicates a loose neutral, like you have.

This is a fairly serious problem, and it needs to be fixed ASAP. It will get worse. Much worse. Maybe suddenly. When it does, it can destroy every electronic device in your home simultaneously, and can cause weird shock hazards like electrified water piping. So get a competent electrician to handle it very soon!
See less See more
  • Like
Reactions: 4
Thanks all for your suggestions. Your ideas are all very neat and make sense. This is a house I rented out so I scheduled a time to go back and execute the ideas you've all suggested for this coming Saturday. I will be sure to update you all with my findings.

Other electrical contractors are telling me they feel a bad neutral may be the cause but I will check first.

Get a different electrical contractor.
And how exactly is that supposed to help me? I don't get ya.
A competent electrical contractor would have been able to diagnose and troubleshoot this problem. It isn't all that uncommon.
The neutral current will not always be the difference of the 2 legs. That would only apply if all loads were 120 Volt. You can have 240 Volt loads that would not have any neutral current.

As for the voltage differences in the 2 legs, you have a bad neutral connection somewhere in the supply chain.

My system voltage here is 125/250. A bit on the high side but that's the way its always been here.
I'm troubleshooting an issue at a house and came across the following rather odd circumstances. I pulled in an electrical contractor with 33 years of experience and even he was dumbfounded and had no answers (said he'd consult other electricians). Just seeking ideas from where ever I have access.

-House is a regular ranch home in the US Midwest with a 100AMP service. Off the bat, we measured the power supply as 244V not 240V (I know it fluctuates as you measure it, but in my 10 years of working on houses I've never seen it go outside the 239-241V range).

-The power supply is not balanced for some reason: One leg on this house has 130V and the other 114V. The current on the neutral is much less than the difference between the currents on the two legs. Specific example: leg 1 had 28A and leg 2 had 4A yet the neutral was not 24A (28-4) it was 18A. Then I checked for current on the ground and baam - the ground was carrying about 6A. Yet I can touch the ground and not get shocked! I measure the voltage on the ground and it is 0V. I verified this to be a good earth ground.

-Initial suspicion was that one of the outlets in the house is wired incorrectly with the neutral going to the ground and vice versa but I checked all the ground wires coming to the panel and none were hot.

Anyone ever experienced anything like this? Any ideas? I'm really confused by how the meter was showing 6A on the ground for the service yet no volts?!? How can there be current without voltage? Or is the voltage so low (less than 0.01V) that my meter could not show it?

If you have a split supply,
the for it to be balanced then you would
need to have exactily the same load on each hot line !
Very unlikely.
To confirm, put an clamp on ammeter on each hot supply,
Good chance that the lower one has more load on it !
The current in the earth line could be due to unbalanced load,
or a bad connecttion somewhere.
Try turning off circuits and see what happens to the meter reading.
And measuring from earth to earth will always give no reading.
This is a house I rented our so I scheduled a time to go back and execute the ideas you've all suggested for this coming Saturday. I will be sue to update you all with my findings.
You need to call a competent electrician to go handle this ASAP. As a landlord, it's your obligation to maintain the property in a safe condition. A loose/open service neutral connection is UNSAFE and you may find yourself with huge expenses for damage to your tenant's property or, worse, injury.
The neutral current will not always be the difference of the 2 legs. That would only apply if all loads were 120 Volt. You can have 240 Volt loads that would not have any neutral current.
Even with 240V loads, the neutral current still works out to the difference between the two legs, since the 240V loads impose equal and opposite current on both legs and can be disregarded:

A panel has the following loads:
240V 4800W = 20A on A and B
120V 600W on A = 5A on A
120V 1200W on B = 10A on B

Current on A: 20+5=25A
Current on B: 20+10=30A
Difference = 5A on neutral
A competent electrical contractor would have been able to diagnose and troubleshoot this problem. It isn't all that uncommon.
Oh I see... except no electrical contractor has actually worked on the problem. I've talked to good ones that I've been using for years on the phone. I haven't called anyone out yet. I can do a lot of electrical stuff myself and have learned a lot over the years, I've wired entire houses, done new and existing service upgrades, etc, definitely wouldn't call myself a pro as I am always working on my own properties but I thought I'd check by myself first and get some ideas from you all as well.

The neutral current will not always be the difference of the 2 legs. That would only apply if all loads were 120 Volt. You can have 240 Volt loads that would not have any neutral current.
Nah you are wrong, as mpoulton just explained above. Maybe what you were trying to say is that the neutral would read 0 if all I had were 240V loads??

If you have a split supply,
the for it to be balanced then you would
need to have exactily the same load on each hot line !
Very unlikely.
To confirm, put an clamp on ammeter on each hot supply,
Good chance that the lower one has more load on it !
The current in the earth line could be due to unbalanced load,
or a bad connecttion somewhere.
Try turning off circuits and see what happens to the meter reading.
And measuring from earth to earth will always give no reading.
The imbalance I was referring to was voltage not current! Re-read my post. The voltage coming in from the utility should be balanced (within reason) between the two legs. You are right regarding current, but that is not what I was referring to. Thanks.

You need to call a competent electrician to go handle this ASAP. As a landlord, it's your obligation to maintain the property in a safe condition. A loose/open service neutral connection is UNSAFE and you may find yourself with huge expenses for damage to your tenant's property or, worse, injury.
I see you state you are a lawyer... well, also to follow your signature, let's stick to construction. I have been in the rental business for years, own too many units that I manage myself and others that I manage which do not belong to me and I know that as the landlord I am not responsible for utility supply issues. I have checked everything from the meter to the house and all is good and secure. I went on the roof and even the connections at the weather head look good. Whatever is causing this is probably somewhere on that neutral along the wire. As it is the ground in the service panel is doing its job.

Bad utility neutral in your service drop to the weather head. Go outside and look at the neutral from the weather head to the transformer and look for broken strands. Your neutral will look like a wire rope. Have you been noticing any dimming and brighting with your lights?
I checked with the tenants and they have not seen anything strange at all. I checked the wire and I didn't see broken strands - I have to admit, it might have been hard to see them anyway.
See less See more
I see you state you are a lawyer... well, also to follow your signature, let's stick to construction. I have been in the rental business for years, own too many units that I manage myself and others that I manage which do not belong to me and I know that as the landlord I am not responsible for utility supply issues. I have checked everything from the meter to the house and all is good and secure. I went on the roof and even the connections at the weather head look good. Whatever is causing this is probably somewhere on that neutral along the wire. As it is the ground in the service panel is doing its job.

I checked with the tenants and they have not seen anything strange at all. I checked the wire and I didn't see broken strands - I have to admit, it might have been hard to see them anyway.
Since I'm not you lawyer, I'm speaking more as a fellow residential landlord and former construction manager. Utility supply issues might not be the landlord's responsibility, but a bad neutral can be either the utility's problem or the customer's. The definitive test is to measure the voltage imbalance at the weatherhead connections, which is usually where the utility's responsibility ends and yours begins. If you measure between the utility's bare neutral and either hot leg at the weatherhead and see a voltage rise when there's a load on the opposite leg, then the problem is definitely at the pole. But if you're seeing balanced voltages at the weatherhead but not in the panel, then there's an issue somewhere in between - like the meter socket.
The imbalance I was referring to was voltage not current! Re-read my post. The voltage coming in from the utility should be balanced (within reason) between the two legs. You are right regarding current, but that is not what I was referring to. Thanks.
There is a link between the two !
The utility puts in x amount of power to the tranny primary.
So that x amount of power should be avaliable(minus losses)
on the secondary split windings.
So if it is reasonably balanced and not overloaded then the
voltages on both legs should be close.
But if there is a larger load on on side,
this will effect the other side.
With same power in, as one requires more power
then there is less available for the other so the voltage
will fall.

You have to look at it from the angle of "power" not volts
to understand it.

Assuming its not a faulty neutral, then it could just be
more load on one side compared to the other.
And it might not be in your panel, it could be caused
by other houses sharing one tranny (a poco problem).
See less See more