running electric to a shed I plan on using a 60 amp from main panel and putting a sub panel in shed question is can i run 2 #10 for hot and then run 2 #14 for the netural and the ground or do they have to be the same size as other wires. my shed is 50 ft from main panel and I already ran underground conduit couple years ago
 

·
Registered
Joined
·
305 Posts
#10 won't do it for 60 amps. How are you running it out there? Individual conductors in conduit will need at least #6. You'll need (3) #6's and I think you may be able to use #10 for the ground but I'll let the others answer that one.
 