"It is worth noting that there is no main vent stack in this house. I cannot tell if the toilet and other pipes have AAVs but the only vent going up to the roof is a 2" vent that comes from the main ejector itself."
This is your problem AAV's do not allow for positive pressure release as a vent to the outside will. So when your pump discharges it will cause trap seals to fail. You need to run a new sump pit vent out the roof or into the current vent going out from the upstairs.