Is there anyway to test the earth ground conductor other than use a meter and wire to reach the ground rod and the panel. I am asking because if you just look in the panel and the ground conductor is connected does not mean it is connected to the ground rod or that it is not broken. Thanks
 

· Registered
Joined
·
423 Posts
Discussion Starter · #4 ·
Maybe I wrote the question wrong. How do you check to see the ground conductor is connected to the ground rod and is not broken anywhere. I am thinking of older installations. Seems that just because the conductor is clamped to the ground rod and the panel ground doesn't seem to be a good verification of the ground network. What if the wire is broken in the wall. Hope this is stated better.
Thanks
 

· Banned
Joined
·
2,487 Posts
The simplest way would be to just run a wire outside and check for continuity between the panel and outside. It would be a very low reading if not zero. Or you could disconnect it (carefully), at say the panel, and take a continuity reading between the ground wire and neutral. It should be very high but not infinite.
 

· Registered
Joined
·
423 Posts
Discussion Starter · #6 ·
Thanks inphase. that is what I was looking for. This is in a 3 story condo and running a wire to the ground rod if I could find it was not a good option.
 