I am renovating my 700 sq ft apartment. It has a 2 ton Skymark HVAC unit that produces 750 CFM for heat and 800 CFM for A/C. The unit is located in a bedroom closet.
There are 2 supplies coming off the HVAC unit supply plenum:
- 16 x 6 rectangular sheet metal duct feeding the bedroom
- 12 x 6 rectangular duct feeding the living room (and remainder of apt), fed by 9" flex duct elbow from the HVAC supply plenum.
If my calculations are correct, the current supply set-up carries ~ 750 CFM.
The bedroom is hot when the heater is on and cold when the a/c is on, so I would like to correct this. Based on the sq. ft. of the bedroom I only need ~160 CFM. I have the following questions:
Could I change the 16 x 6 rectangular bedroom supply to an 8" round flexible duct supply with a damper? This would reduce total apt. supply to 525 with damper open. (According to the Silent Flex II friction loss chart 8" should carry 225 CFM at .1 friction loss)
Will a total CFM supply less than the rated capacity (800 CFM) of the unit damage the HVAC unit / cause the coil to freeze when a/c is running, (especially if I close the damper to achieve ~160 CFM supply in bedroom)?
Unfortunately, the other supply (12 x 6 feeding the living room) is in the ceiling and cannot be changed. The only component of the living room supply that is accessible is the 9" flex duct elbow. Is it correct to assume that increasing the diameter (or to metal) of the elbow will not help because ultimately the supply is limited by the smallest component (in this case, the 12 x 6 rectangular duct)?
Any ideas (I've searched other threads but can't find anything that specifically helps here)?
Thanks is advance for your help.
There are 2 supplies coming off the HVAC unit supply plenum:
- 16 x 6 rectangular sheet metal duct feeding the bedroom
- 12 x 6 rectangular duct feeding the living room (and remainder of apt), fed by 9" flex duct elbow from the HVAC supply plenum.
If my calculations are correct, the current supply set-up carries ~ 750 CFM.
The bedroom is hot when the heater is on and cold when the a/c is on, so I would like to correct this. Based on the sq. ft. of the bedroom I only need ~160 CFM. I have the following questions:
Could I change the 16 x 6 rectangular bedroom supply to an 8" round flexible duct supply with a damper? This would reduce total apt. supply to 525 with damper open. (According to the Silent Flex II friction loss chart 8" should carry 225 CFM at .1 friction loss)
Will a total CFM supply less than the rated capacity (800 CFM) of the unit damage the HVAC unit / cause the coil to freeze when a/c is running, (especially if I close the damper to achieve ~160 CFM supply in bedroom)?
Unfortunately, the other supply (12 x 6 feeding the living room) is in the ceiling and cannot be changed. The only component of the living room supply that is accessible is the 9" flex duct elbow. Is it correct to assume that increasing the diameter (or to metal) of the elbow will not help because ultimately the supply is limited by the smallest component (in this case, the 12 x 6 rectangular duct)?
Any ideas (I've searched other threads but can't find anything that specifically helps here)?
Thanks is advance for your help.