I have an existing 220v line which supplys a outdoor light pole with two 400w metal halide fixtures. How can I drop the voltage down from the 220 supply leaving the fixtures to add a 110v outlet at the base of the pole?
Pulling ONLY a NEUTRAL from the panel will not help you. Because you can't protect a 120v. load with a 2-pole circuit breaker. You have to bring a 2-wire + ground lead from the panel and protect it with a single-pole 15 or 20 amp. breaker, depending on the size of wire and the receptacle. In addition to meeting all the other requirements for outdoor installations by the NEC!!!:yes:Transformer or pull a neutral from the panel
I'd think about that statement again! Under the 2008 NEC Code, Multi-wire branch circuits are required to be protected with a 2 pole breaker. What the op has (with the addition of the neutral wire) is basically a multi-wire branch circuit.Pulling ONLY a NEUTRAL from the panel will not help you. Because you can't protect a 120v. load with a 2-pole circuit breaker. You have to bring a 2-wire + ground lead from the panel and protect it with a single-pole 15 or 20 amp. breaker, depending on the size of wire and the receptacle. In addition to meeting all the other requirements for outdoor installations by the NEC!!!:yes:
He say's it feed's one existing pole,he wants to change it it 120.Pull a neutral, existing pole should be grounded regardless of 120 ,220 or 480 volts.You now have 2 circuits for for a MWBC for your lites just have to make sure it is on 15 or 20 amp breaker.