Are there any code issues involved in drilling holes in a meter pan for attaching fittings?

I'm going to run 12/2 MC to/from the pan and I'd like to wire from the back (it's a finished wall). The smallest KO looks to be about 1", and I'd want 1/2". Also, there's only 1 KO in the back.

(BTW, this is NOT my service meter. I'm installing one in my garage to monitor my wife's Chevy Volt's charging usage -- and no, I'm not billing her :laughing:).
 

· Registered
Joined
·
1,543 Posts
Strictly speaking I believe that one of the things that makes a meter enclosure code compliant is the UL listing, and an alteration like drilling a hole where there was not already a knock-out would invalidate the UL listing of the component. The fittings are a lot cheaper than having to buy another meter socket if this is being done on permit and the inspector objects.
 

· You talking to me?
Joined
·
7,551 Posts
if you own the box and the meter, the only limitations would be if there was weather involved. If this is inside, you can do whatever you want to. If this is outside, you would have to consider the raintight rating and use appropriate fittings and/or be sure you are not restricted to where in the box you can drill and retain the 3R rating.
 

· Electrician
Joined
·
1,404 Posts
Strictly speaking I believe that one of the things that makes a meter enclosure code compliant is the UL listing, and an alteration like drilling a hole where there was not already a knock-out would invalidate the UL listing of the component.
So almost every panel I have worked in is now not CSA or UL listed because I made my own holes?

I say drill away and make a new hole.
 

· You talking to me?
Joined
·
7,551 Posts
So almost every panel I have worked in is now not CSA or UL listed because I made my own holes?

I say drill away and make a new hole.
Oh Gawd, Let's see. There was about 200 panels at that last big job. Then, at that school there was probably close to 100. Damn, there has to be a couple thousand I have to go replace now. Man, what are you supposed to do with the tubs that don't have any knockouts at all? (which is the type I prefer)

just so willk doesn't feel beat up on: I understand his thought and intention but he needs to understand that tubs are designed with the intent they will have holes put in them by the installer. As long as any restrictions the manufacturer puts on the location are observed, it's all good. There are some panels, usually 3R rated panels and things like transformer cases where they require there are no holes drilled above some line within the tub. Other than that, you are generally good to make all the holes you want to make.
 

· DIY'r
Joined
·
523 Posts
Discussion Starter · #10 ·
just so willk doesn't feel beat up on:
Agreed.. I asked originally because my thinking was basically the same as Will's, though I've seen it done on panels but never a meter pan. I guess there's no difference, but I wanted to be sure.

This is indeed going to be an indoor installation, so 3R rating is not an issue.
 

· Registered
Joined
·
1,543 Posts
No problem, my background with UL and CSA is in medical devices and you can affect UL listing by changing nothing but the manufacturing location, even if the exact same design and processes are making the same parts.
 