The solution I would go with is to add a ground bar kit. It should mount to the holes already in the panel, one of which is visible to the left of the paper sticker. Then move all the grounds and you should have enough holes for the neutrals.
Yes it is safe to rearrange the bare grounds and neutrals. Remember that the wires feeding the main breaker from the meter are still live.So the grounds are the bare wires and the neutrals are the white sheathed ones? Are the wires safe to move when I shut off the main power(the one inside this box that does the whole house)?
Sent from my SM-G986U using Tapatalk
I suspect that, as others have mentioned, the panel itself is 'ground' enough*..but yes, you 'can' also run a ground wire between the two, just in case the inspector 'expects' that : )This all makes sense, thank you. Do I need to connect a wire between the two bars or does the bar being screwed into the case provide adequate grounding?
Yes it is safe to rearrange the bare grounds and neutrals. Remember that the wires feeding the main breaker from the meter are still live.So the grounds are the bare wires and the neutrals are the white sheathed ones? Are the wires safe to move when I shut off the main power(the one inside this box that does the whole house)?
Sent from my SM-G986U using Tapatalk
It's interesting you say this, as my main panel outside does NOT have a ground wire to a ground rod. This was actually the other item on my list of things to address.This MAIN service entrance panel also has a Ground wire to an outside Ground ROD, within the ground.
or, be willing to pay an electrician to stop by and add one for you...maybe $100, maybe $300, or somewhere in between... it's a short quick job for them, but your area may dictate what pricing is 'normal', even for small jobs.
it's interesting that the inspector 'expects' these neutrals to each be in their 'own' slot, although nothing was mentioned about the grounds also being within the same bar, even though all grounds and neutrals are on the same 'bar' regardless of whether they are all in their own slots, are they all share a slot with another - it almost doesn't make common sense, but that's what some inspectors 'expect', regardless.
There must be some reason for it, though it alludes me.
noted, but 'what' is the REASONING for the code?It is called a code requirement!
Okay I understand what you are saying. The inspection report said the following. I didnt see a physical rod so I assumed it was not present.that is NOT your MAIN PANEL, that is only your METER - your Main Panel is most likely the large panel IN YOUR HOME - with 100 or 200amp main breakers. This is the panel that will have a 'ground rod' it is attached to, somewhere on your property.
that is NOT your MAIN PANEL, that is only your METER - your Main Panel is most likely the large panel IN YOUR HOME - with 100 or 200amp main breakers. This is the panel that will have a 'ground rod' it is attached to, somewhere on your property.