Double Tapped Breaker

2271 Views 3 Replies 4 Participants Last post by  frenchelectrican
hello all,
at a recent home inspection, the inspector noted that a breaker was double tapped and this is not good because it could arc, one wire is for lights and the other is for the doorbell transformer, he mention i could use a 2 pole breaker like the one pictured here, is this true or safe?? what else could i do with the doorbell wire? put it on another seperate appropriate breaker?
http://www.drillspot.com/pimages/1565/156513_300.jpghttp://www.drillspot.com/pimages/1565/156513_300.jpg
1 - 1 of 4 Posts
Most SqD and CH breakers are listed for doubletapped with two conductors at the termail screw however Double check the label to make sure { they are only allowed on 30 amp or smaller breaker size } I doubt that other are listed like that.

Otherwise just make a pigtail and wirenutted it and that will useally take care the issue there.

Merci,Marc