hi everyone, I'm new here and I was searching for solutions online when I came across this website. I find it very interesting.
I'm a student in electrical electronics engineering, @ 500 level.
in a double pole 100 ampere main breaker, split busbar 240volt at 50hertz supply,
if the current carrying capacity of the sub circuit breakers in either busbars exceed 100amp will the main breaker trip?

or if the current carrying capacity of the the sub circuit breakers in both busbar combine exceed 100amp?

DUSTIN 89
"he who ask is a fool for a short time, he who never ask is a fool forever "
 

· A "Handy Husband"
Joined
·
15,049 Posts
Depends. If the current exceeds the capacity of the branch circuit breaker, that breaker will trip. If the sum total of all the branch circuits exceed 100 amps (without exceeding the capacity of any branch circuit breaker), the main will trip.
 

· Registered
Joined
·
11,194 Posts
I wouldn't try to answer the question as it it not a North American power question. While I've looked at 240v 50hz systems in various countries, I've never seen a 2 pole main on a split bus panel. It is probably a commercial service rather than residential.

Since he didn't specify the "exceed 100 amps" in quanity or time, and we don't have trip curves for his equipment, we don't know how long or if it would trip at x amps above 100amps.
 

· Idiot Emeritus
Joined
·
1,910 Posts
I think what the OP is getting at is 'will an overload on either pole trip the breaker?'

The answer is yes, if one pole is loaded to 2 amps while the other is loaded to 200 amps, the breaker will trip. And if it is a factory assembled 2 pole unit, it'll trip both poles even though only one is overloaded.

Rob
 

· Registered
Joined
·
7 Posts
Discussion Starter · #9 · (Edited)
what I really mean by the questions is
if the actual load of the sub circuit breakers in either busbar exceed 100amp or if the sum the total load of all the sub circuit breakers in both busbar combine exceed 100amp?
can I safely load each side of the busber to 100amp each?

thanks for the reply.
 

· Registered
Joined
·
708 Posts
You can draw up to 200 amps of 120 volts from a 2-pole 100 amp breaker. Or you can draw 100 amps of 240 volts.
You might be surprised about drawing twice the current but actually you are getting the same amount of power (watts).
 

· Registered
Joined
·
2,513 Posts
thank you Joed.
so I can safely load the two sides to 80% each.
but I feel like if I load the two busbar to 100amp each is like I'm loading 200amp in a double pole 100amp main breaker

NEC load calc, but usually adding circuits to a home panel will not cause a problem as most dwelling services are already over sized. Also consider that adding the breaker handles up mean nothing. A 100 amp panel can have over 400 amps worth the breakers.
 