This question is for a friend (yes really). I was over at his home last night and he showed me his newlt built garage. He and his son wired it, they are almost done and need it inspected soon.

He had covers off on a few because he was told the inspector will want to peek inside. Others told him no, he'll take the covers off if he wants.

I noticed that they doubled up on the ground wire to the receptacle. Ground to the metal box and ground coming in are terminated on the same screw on the receptacle. Is this Kosher? I thought it would have been better had they pigtailed and only had one wire on the screw.

What say ye?
(WA State, if it matters)
 

·
Super Moderator
Joined
·
14,012 Posts
One conductor per screw head. The grounds need to be connected to each other and pigtailed to the box and receptacle. Your friend has some work to do.
 

·
Registered
Joined
·
2,786 Posts
I noticed that they doubled up on the ground wire to the receptacle. Ground to the metal box and ground coming in are terminated on the same screw on the receptacle. Is this Kosher? I thought it would have been better had they pigtailed and only had one wire on the screw.
Do you mean like this where the end of the ground is going to the device(switch...receptacle)
 

Attachments

·
custom user
Joined
·
1,074 Posts
Discussion Starter #5
Do you mean like this where the end of the ground is going to the device(switch...receptacle)
Not quite. No bare ground wires for one thing. He has a green wire screwed to the box ground with a spade connector on the other end connected onto the receptacle ground screw, shared with the ground wire coming in from the flex conduit.

It will work but I don't know if it will pass muster.
 

·
custom user
Joined
·
1,074 Posts
Discussion Starter #6
One conductor per screw head. The grounds need to be connected to each other and pigtailed to the box and receptacle. Your friend has some work to do.
Ooops. I apparently scrolled by your post. That's what I thought. Are bare wires a requirement or does it matter?
 

·
Super Moderator
Joined
·
9,102 Posts
Bare wires are not required, but all grounds connected together and one wire under each screw.
 

·
custom user
Joined
·
1,074 Posts
Discussion Starter #9
so the ground screw of the receptacle has two wires under it?
Bare wires are not required, but all grounds connected together and one wire under each screw.
Yes, two wires on the ground screw of the receptacle. Sounds unanimous that it won't fly. I hadn't seen it before so I was skeptical.

Thanks for the input.
 

·
Registered
Joined
·
9,232 Posts
Wait a minute! If wires have spade lugs attached, can't a number of the spade lugs plus one wire curled around the screw share the same screw?
 

·
Registered
Joined
·
189 Posts
JasperST said:
Hey y'all,

This question is for a friend (yes really). I was over at his home last night and he showed me his newlt built garage. He and his son wired it, they are almost done and need it inspected soon.

He had covers off on a few because he was told the inspector will want to peek inside. Others told him no, he'll take the covers off if he wants.

I noticed that they doubled up on the ground wire to the receptacle. Ground to the metal box and ground coming in are terminated on the same screw on the receptacle. Is this Kosher? I thought it would have been better had they pigtailed and only had one wire on the screw.

What say ye?
(WA State, if it matters)
is this the rough inspection, if it is no devices or covers can be installed
 