Check the 50 amp plug and it seems like no power it getting to the plug. The circuit breaker did not trip either. Any other problems I could be missing?
exercise the breaker. Sometimes they trip but the handle does not move.
If using a DMM does not indicate power at recp, then you likely have a bad connection. check all connections(power off)
Check for power at the load side of the breaker,
Could be a faulty breaker.
If there is power on one side of the breaker, (supply side).
But no power on the load side, then it has tripped,
or it is faulty.
1 - 4 of 4 Posts