i plan to use my chimney to exhaust a gas water heater with a 3" duct and a radiator boiler with a 6" duct. there is no soot involved, i.e. only gas burning fumes. my questions are:

1. can i just run the ducts to an unlined brick chimney or do i have to have a liner inside?

2. regardless of the answer to 1., can entry points of the two ducts at the bottom of the chimney be at the same horizontal level or do they need to be one above the other?

thanks
 

· Hvac Pro
Joined
·
25,132 Posts
hi, Yuri!

We use liners every job and we use a smoke pipe of B-vent Wye

like this


How are you running liners?
We get a Pro chimney company to do ours. They bust the base open and install a cleanout and one entry for the furnace and another above it for the water heater. Must be B vent or 2 single wall liners( one inside the other here).
 

· Hvac Pro
Joined
·
25,132 Posts
not sure i wanna drill another couple holes in my wall. will just probably get a liner. where do you buy they and are they just regular ducts? maybe Roof Center?
Must be aluminum or stainless steel non corrosive liner and B vent/ 2 layers thick where I am and sized according to the amount of BTU's of both appliances and the height of the roof/rise and according to the gas code. May want to get a Pro chimney company to do it. If not done properly you can get downdrafts/fumes spilling and pressure switch tripping problems with the furnace.
 

· Hvac Pro
Joined
·
25,132 Posts
Must be aluminum or stainless steel non corrosive liner and B vent/ 2 layers thick where I am and sized according to the amount of BTU's of both appliances and the height of the roof/rise and according to the gas code. May want to get a Pro chimney company to do it. If not done properly you can get downdrafts/fumes spilling and pressure switch tripping problems with the furnace.
Depends on these factors, add the input BTUs from both from the rating plates. Not sure about the code requirements in your area.
 

· Registered
Joined
·
2,331 Posts
Discussion Starter · #12 ·
this is what i've found:

http://www.efireplacestore.com/cpf-68218.html

however, the next question is what type of fittings do i need to terminate both ends of the chimney.

on the inside end, i will need one 6" elbow at the very bottom, for the boiler, and a 6x6x3" tee right above it for the 3" water heater duct. also, will i need anything on the chimney top?

i saw they have many different types of fittings on that web site and i am unsure as to which to get.

also, for the duct inside the house for in between the appliances and the chimney entry, can i just use regular hard duct from home depot? i noticed that the existing 6" duct for the boiler in the basement has firmer joints than regular crimped/taped ones for like a dryer vent and they have screws.
 