Do multi-wire branch circuits REQUIRE a tied 2-pole breaker, and why? What are the risks of not having one?

(Referring to when a 14/3 or 12/3 cable is used to power two circuits with a shared neutral/ground.)

JC
 

·
Super Moderator
Joined
·
8,922 Posts
They either need a 2 pole breaker or an approved handle tie. The dangers could include equipment damage or bodily harm.
 

·
Registered
Joined
·
1,800 Posts
It depends.

If there are only 120V loads and receptacles on the MWBC, two breakers with a factory handle tie will suffice.

If there are any hardwired 240V or 120/240V loads or receptacles (yeah, you can do that on a MWBC that also supports 120V loads)... then the breaker MUST be a 2-pole.

The reason for the latter requirement is that if one leg of the MWBC were to trip for good reason, the 240V load will die of course, however, current will leak through that load causing the tripped hot wire to "float" at 120V. Effectively it would put all 120V loads on the tripped leg in series with the 240V load. This would defeat the purpose of tripping the breaker.
 

·
Registered
Joined
·
131 Posts
Discussion Starter #4
I just opened up a panel and found a MWBC that's been on two separate breakers, not next to each other (but on separate hot legs) for probably over a decade with no known issues. It'd be complicated to fix it (long story), so what are the inherent risks? What's the rationale/reason for them being tied together?

No 220v appliances/receptacles on the circuit. The MWBC is for kitchen outlets.
 

·
Licensed electrician
Joined
·
13,508 Posts
Prior editions of the code only required a common disconnect of the two legs if they landed on the same yoke in a residence. Commercial was different.

If one leg was turned off the neutral c a n carry current form the other leg. To enhance safety the code now wants to ensure both legs are off to eliminate any neutral current on the MWBC.
 

·
Registered
Joined
·
1,997 Posts
So what is the issue with neutral current if there's no potential?
 

·
Registered
Joined
·
3,055 Posts
A good example of how “it works” and “it complies with code” are not always the same thing.
 

·
Registered
Joined
·
111 Posts
So what is the issue with neutral current if there's no potential?
None as long as the neutral remains connected. Another provision of the code requires MWBC neutrals to not be broken if a device is removed, so changing a receptacle or whatever shouldn't break the neutral.
 

·
A "Handy Husband"
Joined
·
12,013 Posts
It depends.

If there are only 120V loads and receptacles on the MWBC, two breakers with a factory handle tie will suffice.

If there are any hardwired 240V or 120/240V loads or receptacles (yeah, you can do that on a MWBC that also supports 120V loads)... then the breaker MUST be a 2-pole.

The reason for the latter requirement is that if one leg of the MWBC were to trip for good reason, the 240V load will die of course, however, current will leak through that load causing the tripped hot wire to "float" at 120V. Effectively it would put all 120V loads on the tripped leg in series with the 240V load. This would defeat the purpose of tripping the breaker.
One more provision, if the MWBC is wired to a single yoke (split wired receptacle), it requires a 2 pole breaker.

Sent from my Lenovo TB-X606F using Tapatalk
 

·
Very Stable Genius
Joined
·
4,207 Posts
Only real risk, IMO, is that someone will turn off 1 breaker and think the outlet
is powered off and safe to work on (replace etc). A shock will inform them of
the 2nd circuit.
A reasonable half measure would be some sort of marking on the panel....perhaps
a thick "[" line between the two breakers.
 

·
Registered
Joined
·
1,800 Posts
Prior editions of the code only required a common disconnect of the two legs if they landed on the same yoke in a residence. Commercial was different.
That rule still stands, and has nothing to do with MWBCs. Here's where you'd use that.

Suppose I install a recep with both tabs broken off. I wire black/white to the top socket, and red/white-red to the bottom socket (/2/2 cable). Down at the panel, I land on a tandem
(1 space/pole 2 breakers). And that's fine because each leg has its own neutral. Definitely not an MWBC, right?

Later, master electrician comes by and needs to service the recep. Plugs in a loud radio, and flips breakers until the radio goes silent. Standard operating procedure, tried and true. See the problem? Master has turned off only half the yoke. Hence the handle-tie requirement: now, the above procedure will work.

If one leg was turned off the neutral c a n carry current form the other leg. To enhance safety the code now wants to ensure both legs are off to eliminate any neutral current on the MWBC.
There's another reason. Requiring use of a factory handle-tie ensures that the MWBC is correctly phased. Factory handle-ties generally won't allow you to position 2 breakers on the same phase. unless you're doing some sort of deranged misuse such as using a 3-pole handle-tie in a split-phase panel.
 

·
Registered
Joined
·
2,329 Posts
Suppose I install a recep with both tabs broken off. I wire black/white to the top socket, and red/white-red to the bottom socket (/2/2 cable). Down at the panel, I land on a tandem
(1 space/pole 2 breakers). And that's fine because each leg has its own neutral. Definitely not an MWBC, right?

Later, master electrician comes by and needs to service the recep. Plugs in a loud radio, and flips breakers until the radio goes silent. Standard operating procedure, tried and true. See the problem? Master has turned off only half the yoke. Hence the handle-tie requirement: now, the above procedure will work.
I have to remember this, thanks. Another scenerio that catches me once in a while (nothing related to MWBC) is also duplex receptacles with the tabs broken off, same circuit but the top is switched and the bottom is unswitched. With the switch off it's easy to assume the breaker has been turned off especially if you have walked back and forth to the panel like 30 times already in order to test things. But it's not off at the bottom until you tried to undo the conductors.
 

·
Red Seal Electrician
Joined
·
346 Posts
Later, master electrician comes by and needs to service the recep. Plugs in a loud radio, and flips breakers until the radio goes silent. Standard operating procedure, tried and true. See the problem?
The problem I see is complacency. A Master electrician carries a volt-tick or meter and checks again before working on it.
 