Do I need an inspection?

1243 Views 5 Replies 4 Participants Last post by  Scuba_Dave
I added 3 outdoor GFCI outlets (intended for light-duty use) and power for an outdoor ceiling fan.

Used 12/2 Outdoor cable, tapped into an existing 20A circuit that was powering 3 outlets in the kitchen.

I live in Tennessee.

Thanks.
1 - 2 of 6 Posts
well, if you get it inspected you will fail....you can't have your kitchen outlets on with outside gfi's...
no, the kitchen outlets can only serve the kitchen, pantry, dining room, breakfast area etc...therefore, you can't put the outside outlets on with this circuit...you need to come off something else, or run a new homerun