I have a sump pump in my basement that is used to pump out water from the washing machine. It is on a GFCI. I am worried that switch off while in use.
 

·
IBEW Electrician
Joined
·
29 Posts
I have a sump pump in my basement that is used to pump out water from the washing machine. It is on a GFCI. I am worried that switch off while in use.
No you do not need a gfci, I would recommend replacing it with a simplex receptacle, on a dedicated circuit!
 

·
Licensed electrician
Joined
·
13,401 Posts
Under the 08 or newer NEC GFI protection is required for receptacles in unfinished basements and crawlspaces. The simplex receptacle exemption has been removed.
 

·
IBEW Electrician
Joined
·
29 Posts
Under the 08 or newer NEC GFI protection is required for receptacles in unfinished basements and crawlspaces. The simplex receptacle exemption has been removed.
If his town/manici has adopted 08 code, ill personally run to your house right now and give you a big hug. :wink:
 

·
Scared Electrician
Joined
·
715 Posts
thats quite a marathon!!
 

·
Licensed electrician
Joined
·
13,401 Posts
Wonder what he would do if the 2011 had been adopted?
 

·
Registered
Joined
·
474 Posts
I have a sump pump in my basement that is used to pump out water from the washing machine. It is on a GFCI. I am worried that switch off while in use.
Depends on where you live. If your going under the 2011 code yes you do need GFCI protection
 

·
Registered
Joined
·
122 Posts
My house was built in 08 with an unfinished basement. the outlets in the open area was a gfi. the outlet for the sump was not.

however when i was finishing my basement as a tem outlet i put the gfi on my sump and it would et it off when in use. i was lucky i cought this because my basket was 3/4 way full.
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
My house was built in 08 with an unfinished basement. the outlets in the open area was a gfi. the outlet for the sump was not.

however when i was finishing my basement as a tem outlet i put the gfi on my sump and it would et it off when in use. i was lucky i cought this because my basket was 3/4 way full.
The GFCI was tripping regularly when the pump operated? Holy crap! That indicates that the pump actually has a ground fault and is leaking current into the water. Modern GFCI's really don't trip without an actual ground fault. The only reason to avoid a GFCI on a sump pump circuit is if you have made a well-considered decision that flooding is more of a hazard than a ground fault. Personally, I would generally favor using a GFCI with some kind of power-off alarm to indicate a trip. If it trips, don't just reset it! There is an electrical problem to be solved.

Submersible pumps do fail, and when they do they leak current into the water. This can be exceedingly dangerous, especially if the pump still operates and gives no indication of a problem. This can electrify the outflow pipes and other metal objects near the sump, as well as the water itself. For me, the insurance of a GFCI on a sump pump is worth the small risk of pump failure. If you're in an area where a sump pump is really critical equipment, you should have a backup pump that doesn't rely on utility power anyway.
 

·
Registered
Joined
·
53 Posts
What specifically has changed? I have a refrigerator, washer and furnace in the basement all with dedicated circuits but no GFCI protection not to mention our dryer. hum.
 

·
DIY Enthusiast
Joined
·
30 Posts
I had a similar situation, but had a chest freezer plugged into the same outlet as the sump pump. I needed to plug in the charger for my battery backup (Basement Watchdog) sump pump, so I changed the single gang box into a dual gang box and added a GFCI on the first receptacle. The sump battery charger has a built-in alarm for power interruption so if the GFCI ever trips, the battery sounds the alarm and prevents my freezer from thawing.
 

·
Licensed electrician
Joined
·
13,401 Posts
What specifically has changed? I have a refrigerator, washer and furnace in the basement all with dedicated circuits but no GFCI protection not to mention our dryer. hum.
The electrical code changed. There used to be an exemption for single receptacles or receptacles in dedicated space behind appliances. This has been removed.
 