Hello,
I'd like to potentially determine the cause for no aux heat during the defrost cycle on our heatpump and correct the strip staging.
Given: I have a Honeywell TH6220 Stat, Trane XL14i condenser and 4TEC3F60B Air Handler with 3 strips BAYhtr3415000. The condenser has an ODT-A, TAYSTAT250B. I have traced the wires and found no shorts.
From what I have read I believe the issue with the Defrost/No Aux Heat is with the following wiring at the ODT---Air Handler:
Air Handler-----ODTa--Condenser
.....................Pin1----X2
.....................Pin2 no wire
W1W2W3------Pin3
Stat----Air Handler
W2-----W1W2W3
It appears that the X2 will only call for aux heat during defrost if the ODTa is closed, it appears to be set around 25 degrees. Shouldn't Pin2 be connected to W2W3 only at the air handler and if it is real cold ODT circuit closes and all heat called for during defrost?
For staging shouldn't W1 be separated from W1W2 and connected to Stat w2? W1W2 connected at Stat to E?
Comments welcome?
I'd like to potentially determine the cause for no aux heat during the defrost cycle on our heatpump and correct the strip staging.
Given: I have a Honeywell TH6220 Stat, Trane XL14i condenser and 4TEC3F60B Air Handler with 3 strips BAYhtr3415000. The condenser has an ODT-A, TAYSTAT250B. I have traced the wires and found no shorts.
From what I have read I believe the issue with the Defrost/No Aux Heat is with the following wiring at the ODT---Air Handler:
Air Handler-----ODTa--Condenser
.....................Pin1----X2
.....................Pin2 no wire
W1W2W3------Pin3
Stat----Air Handler
W2-----W1W2W3
It appears that the X2 will only call for aux heat during defrost if the ODTa is closed, it appears to be set around 25 degrees. Shouldn't Pin2 be connected to W2W3 only at the air handler and if it is real cold ODT circuit closes and all heat called for during defrost?
For staging shouldn't W1 be separated from W1W2 and connected to Stat w2? W1W2 connected at Stat to E?
Comments welcome?