Daisy Chain help!

10009 21
I have 5 light fixtures wired in a daisy chain. I have them wired using 12-2 romex from the breaker to the switch then to each light. So it is sw- L1-L2-L3-L4-L5. I have 120 volts at the switch and each box with the switch on. Now I can't figure out why the lights aren't working. I even broke the chain and just wired the first light still nothing. What am I missing? Thanks
1 - 20 of 22 Posts

· Registered
Joined
·
57 Posts
I have 5 light fixtures wired in a daisy chain. I have them wired using 12-2 romex from the breaker to the switch then to each light. So it is sw- L1-L2-L3-L4-L5. I have 120 volts at the switch and each box with the switch on. Now I can't figure out why the lights aren't working. I even broke the chain and just wired the first light still nothing. What am I missing? Thanks
Do you have a neutral W-W and phase leg BK-BK to the first light? Daisy chain may not be the appropriate word if the circuit from L5 does not return to the switch.
 

· Registered
Joined
·
57 Posts
All of the grounds are grounded to each box at the same point. So I have a ground from the switch, ground that runs to the next light, and ground from the light fixture. All grounded together.
Maybe the wiring from the switch needs looking at. All white wires at the switch will be connected in parallel with one white going to the first light leg along with the switched black wire in the same cable with matching w-w and bk-bk connection in the lamp wiring.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #13 ·
I have checked the bulbs they are good. Have tried 3 different switches, even wired directly without switch where when I flipped the breaker on lights should have lit up. The breaker must be good if I'm getting 120 volts to each light right. I'm stumped I've done several jobs like this with no problem. I'm lost at this point how do I have 120 volts at 5 lights and none of them work?
 

· Registered
Joined
·
57 Posts
I have checked the bulbs they are good. Have tried 3 different switches, even wired directly without switch where when I flipped the breaker on lights should have lit up. The breaker must be good if I'm getting 120 volts to each light right. I'm stumped I've done several jobs like this with no problem. I'm lost at this point how do I have 120 volts at 5 lights and none of them work?
There is a possibility that you may have heated up the lights with a parallel phase leg hooked up at the panel and there will be a 120V reading to ground.
 

· Licensed Pro
Joined
·
1,571 Posts
Check all your connections... from the panel on. You may have a loose connection that will let you read 120V on the meter, but not allow any significant current to flow.
 