Hi all. My questions concern an outdoor light installation where a supposedly knowledgeable installer put in the wrong fixtures for the application and cut off all the grounds.
I recently built a 120' long by 7 foot high masonry fence along one of my property lines. My neighbor wanted to mount lights along the top of the wall, so I routed 12-2 UF cable in the CMU (this is allowable in my jurisdiction). The neighbor chose one of those ubiquitous security fixtures (Lithonia OVT 1501 120) that has a cast aluminum cage around a cylindrical screw-in glass lamp cover, all of which attaches to a gasketed J-box. They are vapor tight but are only rated for ceilings or walls, not as uplights.
The first issue is the fixtures themselves. The glass cover threads into an aluminum base and seats against a neoprene gasket, keeping moisture out of the glass lamp cover. However, when the fixture is mounted in an up position, that same gasket retains water in the socket where the glass threads into the base. The water dissipates either by evaporation or leaks into the J-box if the glass cover isn't properly seated, as was the case in this installation. The neighbor's solution is to drill weep holes and caulk the gap, which will make relamping a joy. This seems like one of those ideas that will work fine until it doesn't anymore. I'm having a hard time convincing him to just get an appropriate fixture.
The second, and bigger issue, is the cut off ground wires. In addition, the hots and neutrals are all only around 1-1/2" long. In a brilliant stroke, the "installer" decided to forego disassembling the fixtures. He simply pulled the fixture wires through the J-box hole, made his connections outside of the fixture, and then attempted to shove the fixture back down over the connections. This ended up nicking the insulation on several of the wires.
The question is how to make a code compliant repair. I'm thinking of hammer drilling a pocket so I can mortar in a weathertight J-box with the open top slightly proud of the cap block. This would give me enough room to splice the ground with a terminal block as well extend the working length of the hots and neutrals. The new fixture could sit atop the J-box, and the splices would be accessible.
Am I being overly cautious on the fixtures? Are there any potential problems with my fix? Thanks in advance for any input on these two issues.
I recently built a 120' long by 7 foot high masonry fence along one of my property lines. My neighbor wanted to mount lights along the top of the wall, so I routed 12-2 UF cable in the CMU (this is allowable in my jurisdiction). The neighbor chose one of those ubiquitous security fixtures (Lithonia OVT 1501 120) that has a cast aluminum cage around a cylindrical screw-in glass lamp cover, all of which attaches to a gasketed J-box. They are vapor tight but are only rated for ceilings or walls, not as uplights.
The first issue is the fixtures themselves. The glass cover threads into an aluminum base and seats against a neoprene gasket, keeping moisture out of the glass lamp cover. However, when the fixture is mounted in an up position, that same gasket retains water in the socket where the glass threads into the base. The water dissipates either by evaporation or leaks into the J-box if the glass cover isn't properly seated, as was the case in this installation. The neighbor's solution is to drill weep holes and caulk the gap, which will make relamping a joy. This seems like one of those ideas that will work fine until it doesn't anymore. I'm having a hard time convincing him to just get an appropriate fixture.
The second, and bigger issue, is the cut off ground wires. In addition, the hots and neutrals are all only around 1-1/2" long. In a brilliant stroke, the "installer" decided to forego disassembling the fixtures. He simply pulled the fixture wires through the J-box hole, made his connections outside of the fixture, and then attempted to shove the fixture back down over the connections. This ended up nicking the insulation on several of the wires.
The question is how to make a code compliant repair. I'm thinking of hammer drilling a pocket so I can mortar in a weathertight J-box with the open top slightly proud of the cap block. This would give me enough room to splice the ground with a terminal block as well extend the working length of the hots and neutrals. The new fixture could sit atop the J-box, and the splices would be accessible.
Am I being overly cautious on the fixtures? Are there any potential problems with my fix? Thanks in advance for any input on these two issues.